What advice can you give concerning running a 3 metre run of mains tails under ground from the meter head to a new CU in a newbuild property (barn conversion)? and what size would you say?
I'm assuming at this stage the earthing will be tncs.

The requirement is 100A and I see in the TLC catalog that 16mm 2-core is specced at 110A.. so could use 2 core with a separate 10mm/16mm earth? or best to go for 25mm 3-core? (big difference in price.. )

Ive used swa before but not in such a size.. or would it be a better option to use ordinary mains tails thru a metal duct?
The only problem I can see with a tube/ducting is to slow bend it upwards at each end and I guess you would still need to bond the tube but not to faff around with terminating it with conductive glands..
Cheers :eek:
 
Under ground or under floor boards with joists etc?

Its will be under ground but obviously theres the up/down drops to and from the two DBs so we're prob talking a total run box to box of around 8metres. The new building isnt built yet, so this is why Ive been asked to suggest best way to supply it.. its from an existing building (barn) but the distributor has yet to run the supply to it. So once thats done, there will be plenty of leeway to dig a trench and run the cables up the wall internally, before floorboards etc are put down,
Having looked up the cost of 2x2 galvanised trunking and end bends, I think Ive answered my own question as to which is cheapest.. !!
 
Id run in an SWA. If I was you id actually look in the book for the CCC of the SWA and not take the ones from the TLC website as gospel as the figures you have quoted from them don't seem right. I haven't looked as onsite atm. The figures you have may be for xlpe at an operating temperature of 90 which means all the terminals would also have to be rated for this also. And the the lower value for the 3core SWA is because that values is for 3phase not single phase and using the third core as a CPC.
 
Last edited:
Its will be under ground but obviously theres the up/down drops to and from the two DBs so we're prob talking a total run box to box of around 8metres. The new building isnt built yet, so this is why Ive been asked to suggest best way to supply it.. its from an existing building (barn) but the distributor has yet to run the supply to it. So once thats done, there will be plenty of leeway to dig a trench and run the cables up the wall internally, before floorboards etc are put down,
Having looked up the cost of 2x2 galvanised trunking and end bends, I think Ive answered my own question as to which is cheapest.. !!

You will need to run SWA either directly buried or in cable ducting, to calculate the required size you need to do your calcs for a cable that is buried as this will reduce the CCC although not much with your short run length (refer to your copy of the BS7671, not a free cable calc site), the depth of which it is buried would be circumstantial regarding the nature and use of the ground you intend to bury it under although gardening equipment, other trades digging in the future all need to be taken into account, I would not be using galv' trunking under any circumstances.

Your earthing requirements would depend on your barn and its construct and whether the other services are supplied in metal.

Ball park guess if your front end is 100amp in your SW/F would be 35mm 3core swa (can't remember 1ph 25mm rating in duct), if this is out of your experience then don't be afraid to employ someone and work alongside them to gain the experience for future reference, don't try wing such a job by using the internet for advice as there may be factors not mentioned that could be important to design.
 
Last edited:

Reply to mains tails via swa in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size...
Replies
6
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
403
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock