I'm always in a dilemma with regards max demand. Often you work it out and it's higher than the the 80A or 60A cut out fuse. However, you know that in reality it is absolutely fine.
I have thought about this in the past when installing electric showers. Now with EVCP's as well it's making me think a bit harder!
The DNO around here will only allow an 80A fuse if meter is inside. Let's give an example of a standard house.
Shower 40A
Cooker 32A
Sockets 32A
Sockets 32A
Garage 16A
Boiler 16A
Lights 6A
Lights 6A
With the osg diversity (which I rarely use for total demand of house hold), you nearly always get >80A. With the 40% rule in the above example you get 72A which is more realistic, but still leaves no room for a 7.4kW EVCP.
Would you fit one anyway, knowing it will be ok?
What would you guys do realistically?
@Gavin John Hyde , you must come across this lots. I realise there is the CT clamp option, but in this standard example is it really necessary?
I have thought about this in the past when installing electric showers. Now with EVCP's as well it's making me think a bit harder!
The DNO around here will only allow an 80A fuse if meter is inside. Let's give an example of a standard house.
Shower 40A
Cooker 32A
Sockets 32A
Sockets 32A
Garage 16A
Boiler 16A
Lights 6A
Lights 6A
With the osg diversity (which I rarely use for total demand of house hold), you nearly always get >80A. With the 40% rule in the above example you get 72A which is more realistic, but still leaves no room for a 7.4kW EVCP.
Would you fit one anyway, knowing it will be ok?
What would you guys do realistically?
@Gavin John Hyde , you must come across this lots. I realise there is the CT clamp option, but in this standard example is it really necessary?