Hi, looking for some advice on 13amp socket outlets in medical location group 2 supplied from IT/IPS transformers.
Completing 5 year EICR on hospital, and at the moment we are not carrying out any tests on above circuits only entering the circuit details and note in operational limitations.
These supplies/circuits are supposed to be checked annually (IMD's and supplementary equipotential bonding) and 3 yearly check on leakage current of output circuits.
As there are no records of above annual and 3 yearly tests being carried out,and the circuits are not coverd under the scope of the EICR are we correct to enter as limitation and pass the responsibility of testing these supplies back to the hospital maintenance team.
Any advice welcome.
 
Leave such installations to the hospital's maintenance dept. You really need to have an in-depth knowledge of these medical rooms, as well as the special testing requirements involved...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Medical Locations Group 2 Operating Theatre
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
ncs1,
Last reply from
Engineer54,
Replies
1
Views
2,088

Advert

Back
Top