S
sam400
Hi all, I ve just bought a S/H megger CM500 tester, I can't get the insulation resistance test to work, I ve tried various different leads, checked the fuses, changed the batteries and it still won't work.
All that happens is you get 3 short beeps and the symbol of a little man/earth flashes in the top corner?
Has any one had this problem? Not sure if i am doing something wrong or if it is faulty?
Sam
Says error is "Earth voltage too high" but I note on p.14 it says it has both three-wire and two-wire IR test modes. Maybe if you had the leads set up for 2-wire but were telling it to do the 3-wire, or possibly vice versa, it might give you an error?
Hi,
As Sintra says, earth voltage too high, and don't forget- 2 wire test set to LN; for three wire you have all the options.
Regards.
Hi thanks for the replies, I 've tried every config of leads and settings and it still does the same thing.
Your right about the symbol meaning earth voltage being too high I found that in the manual but it still doesn't work when it's not connected to an
installation so it can't be that. I am guessing it's faulty!
Next question is where can I get it repaired?
Sam
Where/how did you buy it? If IR test really doesn't work it's not fit for purpose, have you got any comeback to the seller?
I bought it from eBay a few weeks ago but been too busy to even look at it.
You only get 30 day comeback now with eBay and I ve gone over that so will have to get it repaired or sell it for spares.
Would be a shame tho as its a nice bit of kit and in good condition.
Cheers
What happens when you apply the test to a high value resistor. say a 1 meg?
this will tell you if the meter is working... Also measure the voltage applied by the meter during this test...
The results of these tests will tell you if the instrument is working as it should.
Also what happens when you test with no leads plugged into it?
how much did you pay for it ? if it was cheap, might be worth fixing.
I paid £150 for it, megger wanted £380 to fix it, my local megger dealer wanted £30 to look at it then repairs Start at £100 upwards!
ask the calibration centre for a quote to repair.
