I have a big job incomming and I am a bit confused how to do one thing. I am supposed to do full rewiring of an apartment house. First, I need to place a tails from meter to CU. Length of the tail will be up to 25 meters. How am i supposed to ensure protection of this tail and what size of it should I use?
 
Hi Guys!

I have a big job incomming and I am a bit confused how to do one thing. I am supposed to do full rewiring of an apartment house. First, I need to place a tails from meter to CU. Length of the tail will be up to 25 meters. How am i supposed to ensure protection of this tail and what size of it should I use?

Why did you accept the job if you don't know how to do this?
 
You are not permitted to have tails this length ... you will have to have a fused isolator and the CU supply will then be a submains ... then use your cable calcs to assess what size cable you require.
 
Re: Meter tail - CU >25m

You are not permitted to have tails this length ... you will have to have a fused isolator and the CU supply will then be a submains ... then use your cable calcs to assess what size cable you require.
I know i can , but i need to protect that cable with fuse or rcd

- - - Updated - - -

Goshhh... Why do yu hate me so much:/
 
i know and i am checking if yu know.

Be careful how you phrase responses this can be taken a few ways .....

You could be trolling here if you read this one way or actually saying are unsure how to do it and your asking for advice... this info is in the OSG regarding tail length lets hope you are just asking for a refresher as you haven't needed to implement these regs before and its slipped your mind but honestly its easy to look this one up in the BS7671
 
Re: Meter tail - CU >25m

Writing with yu guys is like walking on a broken glAss:/
i know i can chck this and drfinietly i am gonna do it... I just thought we can make perfectly nice conversation here...
 
Re: Meter tail - CU >25m

I know i can , but i need to protect that cable with fuse or rcd

- - - Updated - - -

Goshhh... Why do yu hate me so much:/

We are not against you .. when you ask a question we have to assume you competence and as your profile says you are an electrician this is one of those questions that really is expected of an apprentice at most ... that aside we all have our blonde days so if your going to ask a question try changing your approach.. you'll see a totally different response well except some who find it easy to slate but don't often offer good advice...

E.G.

Hey guys ... im having one of them brain freezes - y consumer unit is 25m away from the cutout so i propose having a 63amp fused isolator next to the cutout and running Xmm cable to CU - does this sound ok ..please advice ;)

.....
Your responses to the same question will be more then helpful if you think on how to word it better.
 
there is a new diy forum maybe this should be sent there, nobody is trying to be offensive but this is basic stuff as darkwood said get your books out and study them.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Meter tail - CU >25m
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
38

Thread Tags

Advert

Thread statistics

Created
Balarizaaf,
Last reply from
tannerselectric,
Replies
38
Views
5,372

Advert

Back
Top