It would be nice to nice to know maximum load of house then apply diversity to calculate max load and actual load. Then you can decide 16mm or 25mm with a fused isolator on both sides would be preferred solution. Otherwise distribution board will need sticker isolate elsewhere. You can calculate load by wattage of appliance divide by 230v to get amps.
Ignore some people on here like to slate more than helping it helps their brain disorder ;-)
 
It would be nice to nice to know maximum load of house then apply diversity to calculate max load and actual load. Then you can decide 16mm or 25mm with a fused isolator on both sides would be preferred solution. Otherwise distribution board will need sticker isolate elsewhere. You can calculate load by wattage of appliance divide by 230v to get amps.
Ignore some people on here like to slate more than helping it helps their brain disorder ;-)

So, if you were to supply the property with a 63A Switchfuse, are you saying that you would you decide the cable size based on diversity? Also, how would you apply discrimination with your "preferred solution" of a fused isolator on both sides of the cable, in addition to the DNO fuse?
Still, as you say, better to ignore some of us with thousands of posts, as our "brain disorder" stops us from talking sense. ;)
 
Re: Meter tail - CU >25m

Going back to the tail length issue though, i was doing a bit in my parents house ( a nearly 2 year old new build) to my surprise (never noticed or paid much attention to it) the meter box was opposite side of the house to the CU, 25mm tails running through stud work, joists etc all backed up by the 100a fuse!! Length of run approx 10meters! Barratt House btw :-)

Why not contact Barratt's and ask them what they are going to do about this non compliance tail installation in your parents house!!
Should be interesting to see what they have to say, as the situation will probably apply to every other house of this type on the development!! lol!!
 
Yep chaps I googled 6181y and even the manufacturers like Batt cable call it double insulated. They then say insulated and sheathed cable! So I stand corrected. Is that pandering to on site terminology??
Guitarist, my point was, has someone who's had a hard time on here posting using a 2nd name because of abuse?
 
Is that pandering to on site terminology??

Precisely, as reference to insulated and sheathed cables as "double insulated" is a nonsense. The sheath is merely to provide mechanical protection, and although it may be made of an insulating material it certainly isn't tested to any standard for that.
 
Yep chaps I googled 6181y and even the manufacturers like Batt cable call it double insulated. They then say insulated and sheathed cable! So I stand corrected. Is that pandering to on site terminology??
Guitarist, my point was, has someone who's had a hard time on here posting using a 2nd name because of abuse?

I don't consider trade banter "abuse" to be honest. Trouble nowadays is that so few go through an apprenticeship, that when anyone says the slightest thing which isn't complimentary, we get told that we're being "harsh" or "abusive". That's the legacy of the modern age.
 
Meter tail - CU >25m

Is this post serious, sounds you don't have a clue how to do it and waiting for someone on here to tell you, r u qualified
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Meter tail - CU >25m
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
38

Thread Tags

Advert

Thread statistics

Created
Balarizaaf,
Last reply from
tannerselectric,
Replies
38
Views
5,372

Advert

Back
Top