Hi all,

I am moving a CU from next to the meter to about 1.5 meters away on an adjacent wall. Am I OK to run the meter tails through the ceiling void between the joists (plasterboard ceiling) to the new CU position or is a case of installing an isolator and 25mm swa?

Many thanks
 
Personally I would be going with a switched fuse, this would allow for a point of isolation and afford the tails some protection rather than relying on the DNO fuse.

Dependant upon the installation method you might be fine with running the tails as they are if not either RCD or SWA.
 
Are the tails coming down the wall surface or buried to the new C.U position or is the C.U to be at high level?
 
Then I don't see any technical reason why you would need swa or a switch fuse.
Thank you for response, I just wasn't 100 per cent about the tails being in the ceiling. So as long as they are coming down the wall surface or are buried at more than 50mm in the wall then that's fine as well?
 
Unless the meter is already at a high level I find it hard to believe the tails will be 3m or less as I generally find - from external meter box to ceiling = 2.5m (includes 0.5m through cavity wall and in meter box)
In ceiling (from what I understand from your post = 1.5m
From ceiling to repositioned consumer unit 0.5m (min)
Total = 4.5m
 
As above, 3m of wire gets used up surprisingly quickly!

I would really check/measure the distances involved first. Have you got pictures and/or a drawing of the planned route?
 
Unless the meter is already at a high level I find it hard to believe the tails will be 3m or less as I generally find - from external meter box to ceiling = 2.5m (includes 0.5m through cavity wall and in meter box)
In ceiling (from what I understand from your post = 1.5m
From ceiling to repositioned consumer unit 0.5m (min)
Total = 4.5m
Yes the meter is also at high level, but yes you're right I will double check the measurements its going to be close to 3m that's for sure
 
As above, 3m of wire gets used up surprisingly quickly!

I would really check/measure the distances involved first. Have you got pictures and/or a drawing of the planned route?
No pics sadly, but yes I will double check, its going to be close to the 3m for sure
 

Reply to Meter tails in ceiling ? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock