Guest viewing is limited
Hi all,
I am moving a CU from next to the meter to about 1.5 meters away on an adjacent wall. Am I OK to run the meter tails through the ceiling void between the joists (plasterboard ceiling) to the new CU position or is a case of installing an isolator and 25mm swa?
Many thanks
Personally I would be going with a switched fuse, this would allow for a point of isolation and afford the tails some protection rather than relying on the DNO fuse.
Dependant upon the installation method you might be fine with running the tails as they are if not either RCD or SWA.
Unless the meter is already at a high level I find it hard to believe the tails will be 3m or less as I generally find - from external meter box to ceiling = 2.5m (includes 0.5m through cavity wall and in meter box)
In ceiling (from what I understand from your post = 1.5m
From ceiling to repositioned consumer unit 0.5m (min)
Total = 4.5m
Total = 4.5m
Yes the meter is also at high level, but yes you're right I will double check the measurements its going to be close to 3m that's for sure
Brighton
Meter tails in ceiling ?
Edders,
Edders,
