MarkieSparkie
Just noticed that the model EICR in the OSG contains at least one mistake ... Nominal Frequency filled in as 150Hz ... I sense an IET corregendum on the way.
No can't agree with that.There is also another anomaly, Observation 6 states "No additional protection to low voltage circuits in bathroom, C3" I think no 30mA RCD or alternatively no supplementary bonding in a 701 special location warrants a C2.
The cut off point was that all installations had to be designed to the 17th from the 1st of July 2008.
Just the same as installations designed from the 1st of January 2012, have to be to the ammendment.