If there was a radial circuit from a 20A MCB then thats fine

If there was a "spur" from a 32A RFC MCB then that is also fine.

It is no different at all to taking a spur off the back of a socket or at any point in the ring via jb.

Pg 362/3
 
the spur should only feed one outletunless fed through 13afcu so max current via 13amp plugs, 26amps.
 
If there was a radial circuit from a 20A MCB then thats fine

If there was a "spur" from a 32A RFC MCB then that is also fine.

It is no different at all to taking a spur off the back of a socket or at any point in the ring via jb.

Pg 362/3


Correct :)
 
If you are spuring a socket, no problem, Nothing can be plugged in greater than 13amps. Assuming a ring main, ring circuit from the board and you wire in 2.5 or above...
But you cannot (or should not) spur off for a 20amp switch or similar, the spur must be a socket or a switch fuse.

Outbuildings are notorious for a 'spur' but some use a 20amp dp switch rather than a switch fuse, thus giving a max of 32amps from origin and still use 2.5 feed.

I have in the past done this but use 6mm, ie use ring main supply breaker at origin, sometimes you need to box clever when on on a budget, I know not ideal but costs sometimes means the job is yours, or not if you insist on a new board. As far as I'm aware there is nothing to stop you doing this, except diiferent size cable should not be used on a breaker/fuse.
However, a small run of cable not more than 300mm to an isolator (attached adjacent the board, wired in 2.5 then outbound in 6mm is ok) as I say not ideal but it is acceptable
 
sorry, maybe its late but i dont get the short run of 2.5 with an isolator? do you mean an fcu or whats protecting the 2.5 cable from carrying 32amps+ for some time.:confused:
 
17th edition onsite guide 7.2.2

Spurs can be connected from a ring at exsiting socket terminals, junction box or source of circuit in dist board.
 
think its down to personal prefernce then.
if it was me running a 2.5 t/e from a cu to a socket below cu then it would be on a correctly rated mcb for the cable thats in the cu.
havent checked the book but does it mention cable size from cu.:confused:
from memory diagram shows interconnections in ring but not directly from cu.:confused:
 
WHAT IS A FORUM WITHOUT DEBATE :confused::confused:

WHETHER IN PICTURES OR WORDS MY INTERPRETATION IS QUITE CLEAR, RIGHT SIZE CABLE FOR THE MCB ;)

I THINK RICHARD EVEN MANAGED TO ANSWER HIS OWN QUESTION SO ALL IS GOOD ME THINKS :cool:
 
I agree with Flukey it is a radial circuit and as there is only 1 earth not 2 as in a ring (which has two t& e thus two means of earth) it would be better not compulsary to lower the breaker/mcb put it on a 20A or 16A if possible not the Immersion though
 