If you are spuring a socket, no problem, Nothing can be plugged in greater than 13amps. Assuming a ring main, ring circuit from the board and you wire in 2.5 or above...
But you cannot (or should not) spur off for a 20amp switch or similar, the spur must be a socket or a switch fuse.
Outbuildings are notorious for a 'spur' but some use a 20amp dp switch rather than a switch fuse, thus giving a max of 32amps from origin and still use 2.5 feed.
I have in the past done this but use 6mm, ie use ring main supply breaker at origin, sometimes you need to box clever when on on a budget, I know not ideal but costs sometimes means the job is yours, or not if you insist on a new board. As far as I'm aware there is nothing to stop you doing this, except diiferent size cable should not be used on a breaker/fuse.
However, a small run of cable not more than 300mm to an isolator (attached adjacent the board, wired in 2.5 then outbound in 6mm is ok) as I say not ideal but it is acceptable
sorry, maybe its late but i dont get the short run of 2.5 with an isolator? do you mean an fcu or whats protecting the 2.5 cable from carrying 32amps+ for some time.:confused:
17th edition onsite guide 7.2.2
Spurs can be connected from a ring at exsiting socket terminals, junction box or source of circuit in dist board.
think its down to personal prefernce then.
if it was me running a 2.5 t/e from a cu to a socket below cu then it would be on a correctly rated mcb for the cable thats in the cu.
havent checked the book but does it mention cable size from cu.:confused:
from memory diagram shows interconnections in ring but not directly from cu.:confused:
WHAT IS A FORUM WITHOUT DEBATE :confused::confused:
WHETHER IN PICTURES OR WORDS MY INTERPRETATION IS QUITE CLEAR, RIGHT SIZE CABLE FOR THE MCB ;)
I THINK RICHARD EVEN MANAGED TO ANSWER HIS OWN QUESTION SO ALL IS GOOD ME THINKS :cool:
I agree with Flukey it is a radial circuit and as there is only 1 earth not 2 as in a ring (which has two t& e thus two means of earth) it would be better not compulsary to lower the breaker/mcb put it on a 20A or 16A if possible not the Immersion though
Calm down.
No point in getting worked up over it:D
HAHAHA, ME, WORKED UP :confused:
MUST BE MISSING SOMETHING HERE JASON AS I AM THE MODEL OF A RATIONAL PERSON. ;)
THE WHOLE IDEA OF A FORUM IS TO ENCOURAGE DEBATE AND IF WE ALL THOUGHT THE SAME AND AGREED, WHAT A DULL PLACE IT WOULD BE.
Guys just for reference there is an update for p362/3 of the regs here:
http://www.------.org/publishing/wi...es/bs7671-2008-corrigendum-jul08.cfm?type=pdf
I think it must be the CAPS then!
I just see it as lazy. If the single 2.5mm T&E for the socket below goes back to the board it ought to either be on a separate breaker or have two pieces of 2.5mm T & E and be part of the ring.
Hey, you can spur off a 1000a busbar if less than 300m, wired in 2.5mm (for alarms etc) so long as fitted adjacent busbar chambre. Many hospitals I have worked on have this arrangement. Point being you cannot run cables outside the area, the spur must be adjoined, hence the 300mm length. By the way I have fitted fire alarms to live 300a busbars, so now can you tell me how I drilled the busbar red...oops brown phase without isolating cos the nat health peeps would not allow isolation, even for a 2 minutes...
All answers please...
Reply to More than one circuit on breaker in the Australia area at ElectriciansForums.net
Last year we purchased a home that was built in the late 1990s It has one outbuilding, sort of a barn/shed about 160 feet from the house (and...
  • Locked
5K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...