Discuss Motor Tripping RCD but it's not even connected to it in the UK Electrical Forum area at ElectriciansForums.net
Yes I appreciate that Westy, but the OP has mentioned in his post that the cb for the motor is fed from the main switch, or I think that's what he means#10.It is a TT system needs rcd for fault protection.
Loading should not trip an RCD.Is it possible to move the problem circuit to between the Main switch and the 1st RCD? might stop the heavy load affecting the RCDs. Or possibly fit another small non RCD ccu just for that circuit?
Loading should not trip an RCD.
Not impossible I have had rcbos tripping the adjacent device on Memshield 2 boards, rcds seem to defy logic.I don't... I think it could be as simple as the quick trip magnetic coil in the MCB interfering with the toroidal inductor in the RCD. Hence my question about placement of devices
But I'm happy to be wrong as then I'll probably learn something
You stole my idea from post #6...I don't... I think it could be as simple as the quick trip magnetic coil in the MCB interfering with the toroidal inductor in the RCD. Hence my question about placement of devices
But I'm happy to be wrong as then I'll probably learn something
I don't... I think it could be as simple as the quick trip magnetic coil in the MCB interfering with the toroidal inductor in the RCD. Hence my question about placement of devices
But I'm happy to be wrong as then I'll probably learn something
You stole my idea from post #6...
a. Can you discover insulation resistance faults on the tripping RCD's final circuits?
I don't have a photo of it but from left to right it is main switch, RCD 1 63A 30mA, 5 MCB's RCD protected, RCD 2 63A 30mA (this is the one that trips), 3 MCB's RCD protected, 32A MCB feeding motor, 16A MCB feeding different motor both 32A and 16A MCB's fed directly from main switch. Mainly old installation, new board, installation fully tested all OK, 2 new circuits for the motors. No borrowed neutrals, definite separation between busbars. Even if the three circuits breakers fed from RCD 2 are switched off the RCD still trips when the bigger motor starts, nothing trips when smaller motor starts. TT system. Brand new motors.