Hello everyone,

A new small DB will be installed inside a garage for few lights and sockets. The feed will come from inside the house. Does it need to be an IP65 unit or can be the usual metal clad?

Thank you
 
Depends on if you think a metal clad is inappropriate for the environment. Either is fine.
 
Unless it is near a doorway where rain could get in (say 45 deg angle), or a known leaky roof, or where someone uses a sink/pressure washer, then I would not worry about meeting IP65.

But if it is only lights and a couple of sockets, and the house CU is already on RCD or RCBO supply, then why not just feed the sockets directly as a radial from a 20A supply and have a 3A FCU to switch the lights off that?
 
Unless the garage is attached to the main house. In which case the new consumer unit should probably be made of non combustible material.
Unless the garage is not part of the domestic premises

1618424481799.png

and is not meant to be used by the people who live in the house, then 421.1.201 applies, whether it's attached or not.
 
Unless the garage is not part of the domestic premises

View attachment 84646
and is not meant to be used by the people who live in the house, then 421.1.201 applies, whether it's attached or not.
Fair point.
There was an article in one of the trade journals considering this. It suggested there may be a case for not applying 421.1.201 in out buildings that are not directly attached to the house.
But it depends, like so many things, on how we interpret the regulations...
 
Fair point.
There was an article in one of the trade journals considering this. It suggested there may be a case for not applying 421.1.201 in out buildings that are not directly attached to the house.
Hard to think what that case might be apart from "we don't want to have to apply it."


But it depends, like so many things, on how we interpret the regulations...
I tend to come down on the side of "interpreting" things on the basis of what the actual words are and what the definitions of those words are.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
New consumer unit for garage
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
Cooper_day,
Last reply from
i=p/u,
Replies
11
Views
2,379

Advert

Back
Top