Hi Guys,

Can somebody shed any light on why socket outlets rated at 32Amps or greater do not require RCD protection under BS7671?

Presumably theres some maths behind it?

And presumably the only exception is in a TT earthing System?

Cheers chaps
 
That was my thinking too. And isn't the disconnection time for such sockets 5 seconds rather than 0.4 seconds? Does not answer the original question, but probably has some relevance.
 
not sure of the answer to that, so will not risk giving you the wrong advice.
 
It's all to do with reg 411.3.x which is about as clear as mud. It's one of those regulations that gives specific guidance for a particular application (sockets less than 32A) without being clear about how to go about installing anything other than that. Suggest you try posing your query in the IET forums - you may get a full answer from the bods on there (or you may not :D)
 
411.3.3
In AC systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
(i) socket outlets with a rated current not exceeding 20A ......
(ii) mobile equipment with a current rating not exceeding 32A for use outdoors

though quite what kind of mobile equipment exists that is rated at over 32A is beyond me
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

spud1

Arms
-
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
No RCD protection for socket outlets rated 32A or greater
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
spud1,
Last reply from
Rampage,
Replies
9
Views
7,545

Advert

Back
Top