Afternoon all...

I would like to experience phantom voltage!! Is there any way I can reproduce it so that I can test it?

I know this might sound a little silly, and I realise my new Drummond test lamp would simply not light up if it is phantom voltage, but I would just like to see it for myself on something that I know for certain is phantom voltage.

I also want to test the digital and analog volt meter on it so I can see what they record.

Again... I know this sounds daft but I just want to see it for myself.

Cheers guys.
 
You can probably "see" this in your own home.

Locate a circuit, turn it off at the CU then attach your MFT - you will probably "see" the phantom voltage as long as the cable(s) run parallel to live circuit(s)
 
Not sure, haven't tried it, but if you took a nice length of three core and earth and wired it up to a load leaving the one middle core unconnected then you should get a "phantom voltage" on the unconnected core.
 
My idea works every year...!!!

14424_4666814865355_968587461_n.jpg
 
You'll get a much larger phantom voltage if you wire a simple circuit using two twin and earth cables. Put a plug on one end of each of them but only connect the live in one plug and the neutral in the other, leave the other conductor unconnected.

Phantom.jpg

If you use a nasty cheap multimeter which should have a ridiculously high input resistance you'll see a substantial phantom voltage between the unused conductors and earth.
 
Now thats exciting Marvo!

I'll let you know how it goes :smile5:
 
Posted a couple of times about an easy way of demonstrating this...Get a length/roll of t&e,expose conductors at each end. Connect L and N at one end. At other end,measure between cpc/N or cpc/known earth. By using differing test instruments,the results can demonstrate both the merits of individual instruments,and,the reason why readings can occur. Also,by adding "links",of varying impedance,between sections of the circuit,you can replicate what you would encounter on an installation,and greatly assist the understanding of results. As incredibly sad as it sounds,some of the most fun i had,as a teenager,was setting up such arrangements,on a large 8' x 4' board,with all manner of purloined items,and inventing faults and scenarios,to test and understand. I suppose a modern risk assessment of such an enterprise,would today prove "troublesome" :bobby:
 
I have to admit that in my 22 year naval career I have never found nor heard of phantom voltages to be a problem. We had 'Wibers' for voltage checking, a version of a drummond lamp, but they were few and far between onboard, and most of us had to rely on our fluke multimeters to check for voltages. (I am well aware they exist).

A far more dangerous problem I feel is the 2mm tip rule and shrouds. If I do not get a voltage and expect one, I have always usually expected it to be there and if not have a damn good check. Nowadays with 'shrouds' I inevitably get some non contacts, and I will investigate further. I wonder if a 'churned out' Electrical Trainee would immediately assume safely isolated. The so called safety of shrouded tips is possibly actually a danger.
 
I have to admit that in my 22 year naval career I have never found nor heard of phantom voltages to be a problem. We had 'Wibers' for voltage checking, a version of a drummond lamp, but they were few and far between onboard, and most of us had to rely on our fluke multimeters to check for voltages. (I am well aware they exist).

A far more dangerous problem I feel is the 2mm tip rule and shrouds. If I do not get a voltage and expect one, I have always usually expected it to be there and if not have a damn good check. Nowadays with 'shrouds' I inevitably get some non contacts, and I will investigate further. I wonder if a 'churned out' Electrical Trainee would immediately assume safely isolated. The so called safety of shrouded tips is possibly actually a danger.


Agreed.

take em off every time.

H&S gone mad
 
Obviously,the base line for these directives,are the lowest common denominator,but 2mm will not prevent someone without training and experience,from doing harm/damage. I have the same regard for safety catches on shotguns...i have NEVER,nor would i ever,use one. If you have to rely on that sliver of metal,that may or may not function,to prevent a gun going off when it should not,you do NOT know your job. It is the faith in these devices,that kids people in to believing, basic training can be skipped. Or...i suppose we could ignore the safe distance from the car in front,and just pop a neck-brace on every time we venture out...:conehead:
 
Obviously,the base line for these directives,are the lowest common denominator,but 2mm will not prevent someone without training and experience,from doing harm/damage. I have the same regard for safety catches on shotguns...i have NEVER,nor would i ever,use one. If you have to rely on that sliver of metal,that may or may not function,to prevent a gun going off when it should not,you do NOT know your job. It is the faith in these devices,that kids people in to believing, basic training can be skipped. Or...i suppose we could ignore the safe distance from the car in front,and just pop a neck-brace on every time we venture out...:conehead:

Just to contradict myself, I do remember live testing a faulty SFC using a meter with lengthy probes. The ship bucked, I slipped, and next thing I was snapping the tip off my now welded probe. So I can see the point in certain situations, and having shrouds on where necessary is a good thing. But I think relatively untrained personnel are far too likely to take a negative reading as fact when having the shrouds on permanently.
 
Just to contradict myself, I do remember live testing a faulty SFC using a meter with lengthy probes. The ship bucked, I slipped, and next thing I was snapping the tip off my now welded probe. So I can see the point in certain situations, and having shrouds on where necessary is a good thing. But I think relatively untrained personnel are far too likely to take a negative reading as fact when having the shrouds on permanently.
The EXACT same thing,happened to me.........only i was trying to get some tomato soup out of a flask,out at Wolf rock...:icon12:
 
Not sure, haven't tried it, but if you took a nice length of three core and earth and wired it up to a load leaving the one middle core unconnected then you should get a "phantom voltage" on the unconnected core.

Well I went with your suggestion Richard, I used approx 30m's of 3 core and earth and popped a plug on the end. Live brown, neutral grey and black was the test conductor (left unconnected) to see if any induced voltage showed up.

Here are the results : (all results are voltage from black - N)

1. Fluke Multimeter (Thanks again Paul :smile5:) shows 91.7V.

Fluke Multi 91.7V.jpg

2. Fluke T5 shows 73V

Fluke T5 73V.jpg

3. Metrel shows 68V

Metrel 68V.jpg

4. Analog shows 37V

Analog multi 37V.jpg

5. Drummond shows <50V (no light)

Drummond 0V.jpg

It was all quite interesting! Quite a range of results from all the testers. It was good to witness first hand phantom voltage and to see the Drummond in action.

I was surprised to see any voltage on the analog meter though, it showed between 35-50V!
 
Last edited:
Well I went with your suggestion Richard, I used approx 30m's of 3 core and earth and popped a plug on the end. Live brown, neutral grey and black was the test conductor (left unconnected) to see if any induced voltage showed up.

Here are the results : (all results are voltage from black - N)

1. Fluke Multimeter (Thanks again Paul :smile5:) shows 91.7V.

View attachment 29152

2. Fluke T5 shows 73V

View attachment 29153

3. Metrel shows 68V

View attachment 29154

4. Analog shows 37V

View attachment 29155

5. Drummond shows <50V (no light)

View attachment 29156

It was all quite interesting! Quite a range of results from all the testers. It was good to witness first hand phantom voltage and to see the Drummond in action.

I was surprised to see any voltage on the analog meter though, it showed between 35-50V!

The input impedance of analogue multimeters can vary considerably. Older ones (AVO 8, etc.) are relatively low impedance and less susceptible to picking up stray voltage, but modern types (used to be called FET input types when this was a novel thing!) can have very high input impedances and be nearly as bad as digital types for stray voltages. Daz
 
The next exercise is to account for those readings and compute the inter-core capacitances per metre of cable. If you know the input impedance of each meter, you can use the change in measured voltage from one to another to determine the effective source impedance of the phantom voltage, and what the open-circuit voltage on the black core would be in the absence of any meter. Don't forget that the impedance driving the test core of the cable is mostly capacitive and the meter input mostly resistive so their voltages are around 90° out of phase, hence the squares of their voltages add, not the voltages themselves.

Then look at the construction of the cable and estimate how that is made up from the various mutual capacitances and resistances between each core and another, and from that characterise the cable. You could then take use that data to predict the stray voltage on a different core with a different layout of energised cores, and compare with the actual result.

You can have hours of fascinating fun with half a roll of T+E!
 
The next exercise is to account for those readings and compute the inter-core capacitances per metre of cable. If you know the input impedance of each meter, you can use the change in measured voltage from one to another to determine the effective source impedance of the phantom voltage, and what the open-circuit voltage on the black core would be in the absence of any meter. Don't forget that the impedance driving the test core of the cable is mostly capacitive and the meter input mostly resistive so their voltages are around 90° out of phase, hence the squares of their voltages add, not the voltages themselves.

Then look at the construction of the cable and estimate how that is made up from the various mutual capacitances and resistances between each core and another, and from that characterise the cable. You could then take use that data to predict the stray voltage on a different core with a different layout of energised cores, and compare with the actual result.

You can have hours of fascinating fun with half a roll of T+E!

Blimey Lucien, is the telly broke? :-) Daz
 
I haven't got a telly, at least not one that gets all the modern programmes! And all I can get on the PC screen this evening is invoices and quotes...
 
The next exercise is to account for those readings and compute the inter-core capacitances per metre of cable. If you know the input impedance of each meter, you can use the change in measured voltage from one to another to determine the effective source impedance of the phantom voltage, and what the open-circuit voltage on the black core would be in the absence of any meter. Don't forget that the impedance driving the test core of the cable is mostly capacitive and the meter input mostly resistive so their voltages are around 90° out of phase, hence the squares of their voltages add, not the voltages themselves.

Then look at the construction of the cable and estimate how that is made up from the various mutual capacitances and resistances between each core and another, and from that characterise the cable. You could then take use that data to predict the stray voltage on a different core with a different layout of energised cores, and compare with the actual result.

You can have hours of fascinating fun with half a roll of T+E!

I was just about to do all of that Lucien :innocent:
 
It was a completely serious suggestion. Only a basic understanding of AC circuit theory is needed to solve most of the mysteries that show up on the forum including ones about phantom voltage, all the calcs can be done accurately enough on a smoke packet. If more sparks turned their minds to solving problems in odd moments and applying equations they learned in college to real life situations, we'd have less dopey questions about why 100k IR doesn't trip an RCD. I'm not tarring you with the same brush BTW. You've gone the extra mile to investigate which most wouldn't.
 
It was a completely serious suggestion. Only a basic understanding of AC circuit theory is needed to solve most of the mysteries that show up on the forum including ones about phantom voltage, all the calcs can be done accurately enough on a smoke packet. If more sparks turned their minds to solving problems in odd moments and applying equations they learned in college to real life situations, we'd have less dopey questions about why 100k IR doesn't trip an RCD. I'm not tarring you with the same brush BTW. You've gone the extra mile to investigate which most wouldn't.
ill be honest but people dont really cover resistors much at college anymore.

i would have liked to have done electronics at college but couldn't
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Odd request regarding phantom voltage!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
31
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
markc123,
Replies
31
Views
6,241

Advert

Back
Top