Afternoon all...

I would like to experience phantom voltage!! Is there any way I can reproduce it so that I can test it?

I know this might sound a little silly, and I realise my new Drummond test lamp would simply not light up if it is phantom voltage, but I would just like to see it for myself on something that I know for certain is phantom voltage.

I also want to test the digital and analog volt meter on it so I can see what they record.

Again... I know this sounds daft but I just want to see it for myself.

Cheers guys.
 
I have to admit that in my 22 year naval career I have never found nor heard of phantom voltages to be a problem. We had 'Wibers' for voltage checking, a version of a drummond lamp, but they were few and far between onboard, and most of us had to rely on our fluke multimeters to check for voltages. (I am well aware they exist).

A far more dangerous problem I feel is the 2mm tip rule and shrouds. If I do not get a voltage and expect one, I have always usually expected it to be there and if not have a damn good check. Nowadays with 'shrouds' I inevitably get some non contacts, and I will investigate further. I wonder if a 'churned out' Electrical Trainee would immediately assume safely isolated. The so called safety of shrouded tips is possibly actually a danger.


Agreed.

take em off every time.

H&S gone mad
 
Obviously,the base line for these directives,are the lowest common denominator,but 2mm will not prevent someone without training and experience,from doing harm/damage. I have the same regard for safety catches on shotguns...i have NEVER,nor would i ever,use one. If you have to rely on that sliver of metal,that may or may not function,to prevent a gun going off when it should not,you do NOT know your job. It is the faith in these devices,that kids people in to believing, basic training can be skipped. Or...i suppose we could ignore the safe distance from the car in front,and just pop a neck-brace on every time we venture out...:conehead:
 
Obviously,the base line for these directives,are the lowest common denominator,but 2mm will not prevent someone without training and experience,from doing harm/damage. I have the same regard for safety catches on shotguns...i have NEVER,nor would i ever,use one. If you have to rely on that sliver of metal,that may or may not function,to prevent a gun going off when it should not,you do NOT know your job. It is the faith in these devices,that kids people in to believing, basic training can be skipped. Or...i suppose we could ignore the safe distance from the car in front,and just pop a neck-brace on every time we venture out...:conehead:

Just to contradict myself, I do remember live testing a faulty SFC using a meter with lengthy probes. The ship bucked, I slipped, and next thing I was snapping the tip off my now welded probe. So I can see the point in certain situations, and having shrouds on where necessary is a good thing. But I think relatively untrained personnel are far too likely to take a negative reading as fact when having the shrouds on permanently.
 
Just to contradict myself, I do remember live testing a faulty SFC using a meter with lengthy probes. The ship bucked, I slipped, and next thing I was snapping the tip off my now welded probe. So I can see the point in certain situations, and having shrouds on where necessary is a good thing. But I think relatively untrained personnel are far too likely to take a negative reading as fact when having the shrouds on permanently.
The EXACT same thing,happened to me.........only i was trying to get some tomato soup out of a flask,out at Wolf rock...:icon12:
 
Not sure, haven't tried it, but if you took a nice length of three core and earth and wired it up to a load leaving the one middle core unconnected then you should get a "phantom voltage" on the unconnected core.

Well I went with your suggestion Richard, I used approx 30m's of 3 core and earth and popped a plug on the end. Live brown, neutral grey and black was the test conductor (left unconnected) to see if any induced voltage showed up.

Here are the results : (all results are voltage from black - N)

1. Fluke Multimeter (Thanks again Paul :smile5:) shows 91.7V.

[ElectriciansForums.net] Odd request regarding phantom voltage!

2. Fluke T5 shows 73V

[ElectriciansForums.net] Odd request regarding phantom voltage!

3. Metrel shows 68V

[ElectriciansForums.net] Odd request regarding phantom voltage!

4. Analog shows 37V

[ElectriciansForums.net] Odd request regarding phantom voltage!

5. Drummond shows <50V (no light)

[ElectriciansForums.net] Odd request regarding phantom voltage!

It was all quite interesting! Quite a range of results from all the testers. It was good to witness first hand phantom voltage and to see the Drummond in action.

I was surprised to see any voltage on the analog meter though, it showed between 35-50V!
 
Last edited:
Well I went with your suggestion Richard, I used approx 30m's of 3 core and earth and popped a plug on the end. Live brown, neutral grey and black was the test conductor (left unconnected) to see if any induced voltage showed up.

Here are the results : (all results are voltage from black - N)

1. Fluke Multimeter (Thanks again Paul :smile5:) shows 91.7V.

View attachment 29152

2. Fluke T5 shows 73V

View attachment 29153

3. Metrel shows 68V

View attachment 29154

4. Analog shows 37V

View attachment 29155

5. Drummond shows <50V (no light)

View attachment 29156

It was all quite interesting! Quite a range of results from all the testers. It was good to witness first hand phantom voltage and to see the Drummond in action.

I was surprised to see any voltage on the analog meter though, it showed between 35-50V!

The input impedance of analogue multimeters can vary considerably. Older ones (AVO 8, etc.) are relatively low impedance and less susceptible to picking up stray voltage, but modern types (used to be called FET input types when this was a novel thing!) can have very high input impedances and be nearly as bad as digital types for stray voltages. Daz
 
The next exercise is to account for those readings and compute the inter-core capacitances per metre of cable. If you know the input impedance of each meter, you can use the change in measured voltage from one to another to determine the effective source impedance of the phantom voltage, and what the open-circuit voltage on the black core would be in the absence of any meter. Don't forget that the impedance driving the test core of the cable is mostly capacitive and the meter input mostly resistive so their voltages are around 90° out of phase, hence the squares of their voltages add, not the voltages themselves.

Then look at the construction of the cable and estimate how that is made up from the various mutual capacitances and resistances between each core and another, and from that characterise the cable. You could then take use that data to predict the stray voltage on a different core with a different layout of energised cores, and compare with the actual result.

You can have hours of fascinating fun with half a roll of T+E!
 
The next exercise is to account for those readings and compute the inter-core capacitances per metre of cable. If you know the input impedance of each meter, you can use the change in measured voltage from one to another to determine the effective source impedance of the phantom voltage, and what the open-circuit voltage on the black core would be in the absence of any meter. Don't forget that the impedance driving the test core of the cable is mostly capacitive and the meter input mostly resistive so their voltages are around 90° out of phase, hence the squares of their voltages add, not the voltages themselves.

Then look at the construction of the cable and estimate how that is made up from the various mutual capacitances and resistances between each core and another, and from that characterise the cable. You could then take use that data to predict the stray voltage on a different core with a different layout of energised cores, and compare with the actual result.

You can have hours of fascinating fun with half a roll of T+E!

Blimey Lucien, is the telly broke? :) Daz
 
I haven't got a telly, at least not one that gets all the modern programmes! And all I can get on the PC screen this evening is invoices and quotes...
 
The next exercise is to account for those readings and compute the inter-core capacitances per metre of cable. If you know the input impedance of each meter, you can use the change in measured voltage from one to another to determine the effective source impedance of the phantom voltage, and what the open-circuit voltage on the black core would be in the absence of any meter. Don't forget that the impedance driving the test core of the cable is mostly capacitive and the meter input mostly resistive so their voltages are around 90° out of phase, hence the squares of their voltages add, not the voltages themselves.

Then look at the construction of the cable and estimate how that is made up from the various mutual capacitances and resistances between each core and another, and from that characterise the cable. You could then take use that data to predict the stray voltage on a different core with a different layout of energised cores, and compare with the actual result.

You can have hours of fascinating fun with half a roll of T+E!

I was just about to do all of that Lucien :innocent:
 
It was a completely serious suggestion. Only a basic understanding of AC circuit theory is needed to solve most of the mysteries that show up on the forum including ones about phantom voltage, all the calcs can be done accurately enough on a smoke packet. If more sparks turned their minds to solving problems in odd moments and applying equations they learned in college to real life situations, we'd have less dopey questions about why 100k IR doesn't trip an RCD. I'm not tarring you with the same brush BTW. You've gone the extra mile to investigate which most wouldn't.
 

Reply to Odd request regarding phantom voltage! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
188
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
579
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
537

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
970
  • Question
Second Update: 12/25/2023 Hey everyone, so I solved my doorbell issue. Turns out there were two reasons why my doorbell wasn't turning on. 1.)...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top