Right then this has now happened to me twice.. and ive not a clue whats going on so if anyone has had the same issue it would be good to see what causing it.

Anyways SO i have a 2G2W light switch upstairs and a 2G2W light switch downstairs.. I Wire them both correct.. Up have Brown from 3-core in Common, then black in L1 and grey in L2 and Live in in L1 and Live out in L2.. that controls the lights on the stairs..

Then i do exactly the same with the upstairs lights. Feed in, feed out L1 + L2 etc.. ok all simple so far..

NOW COMES THE CONFUSING BIT..

The stair lights are working fine on the 2-way wikid..
The LED spotlights in the celing dont work.. OK

SO i swap the cables, basically swapping the switch.. NOW the LED spotlights work on the 2-way but the stair lights dont..

OK so maybe the switch is broke.. Change the switch (TWICE still dosent work)..

Umm maybe i have a strapper down or something.. Bell out the strappers.. BELL OUT FINE.. ok now WHAT the hell is going on here??????? Switch is fine, strappers fine and if i move the strappers from one switch to the other it works so this proves that the Live IN to switch and the Live to the light works an that all the lamps are working..

any ideas anyone?

cheers
 
Broken tester, the Common link brown of 3-core belled out fine with my tester.. But when i put pressure on anything with the probes it belled out fine.. I pressed one down on a wall and the other on my arm and it said it was a circuit

SO the issue wasnt as simple as all put out to be, cable belled out fine BUT due to testers being broken wasnt fine therefore that was the issue

Sorry for late reply been busy

Hum....

With 3 or 4 other sparkies on hand didn't you try another tester? to see what readings they got.

Not convinced, sorry mate
 
Its a brand spanking new fluke one

So there was no real thought going through our heads that it was going to be anything to do with the testers

Fluke T120 Voltage & Continuity Tester Brand New
 
Not convinced either, load of rubbish in my opinion,
first year apprentice could have come up with a better lie.

I hate bullying axel and hope you don't think I'm jumping on the band wagon fella, but 100% agree with will here, it really is school boy stuff, basically the fact 4 sparks looked at this seems ridiculous, I'm almost at a loss to be honest here, 2 way switching is very very simple and a meter wouldn't be needed IMO to solve this problem, I am not trying to bully you at all but come on lets have the truth here, please just tell us what really happened.
 
Bottom line is how long would it have taken to remove the line and switched line, replace them with 2 short tails and set your tester to R2 and check the continuity/switches out? - me thinks no more than 15 minutes

Belling out is no replacement for checking the R2 values - especially as you could check the switches and the cable with the same test.
 
The only thing i can say was it was at 4:30pm when it was found and we leave at 4:00 and Dont get paid overtime.. So was all ready to leave anyway.

But like say wired so many of these, done much larger scale ones etc and never had a single issue so was bizarre to suddenly come across this with broken test leads.

You would be lucky to get someone like me ;) HA >.>
 
The only thing i can say was it was at 4:30pm when it was found and we leave at 4:00 and Dont get paid overtime.. So was all ready to leave anyway.

But like say wired so many of these, done much larger scale ones etc and never had a single issue so was bizarre to suddenly come across this with broken test leads.

You would be lucky to get someone like me ;) HA >.>


As I mentioned I won't tolorate any bullying myself and therefore after your explanation whether I believe it or not now bow out of the thread, I still think it is ridiculous 4 sparks couldn't sort it out but won't mock you, all the very best axel, chin up.
 
I'm confused how broken test leads were closed circuit, if lead damaged wouldn't it work correctly or be open circuit?? I can't see how it's possible for the damaged leads to show continuity, or have I missed something..... At least the thread title is 100% correct..one to confuse you all!! Lol
 
Its a brand spanking new fluke one

So there was no real thought going through our heads that it was going to be anything to do with the testers

Fluke T120 Voltage & Continuity Tester Brand New

Don't take any notice of these reprobates. They are still in Friday evening mode.......

Well done ! I had the same problem myself in the middle of an assessment. Just as well I had a spare set of leads... hint, hint and sloved the problem pdq without embarrassment I ripped them apart to find the earth lead had become disconnected.
I now have two sets of leads.....
 

Reply to One to confuse you all!! in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K
Thank you! I didn't realise the wiring was QUITE that old… I'll replace it carefully.
Replies
2
Views
311

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top