Open end to end readings on ring main on rn r2 - where should this go under in schedule of inspections
using napit software doing a DEICR
C2?
 
There is no specific observation for ring circuit continuity.

You could maybe use "connections soundly made..." Under. 5.17.

Reg. 643.2.1 applies.
 
It's not the result of an inspection but of testing so the Schedule of Inspections isn't relevant to the observation.
 
im on the napit fast test certificate so doesnt show that
Ah ok. Have you got:
5.5 Adequacy of cables for current-carrying capacity with regard for the type and nature of installation (Section 523)

As effectively you have two undersized radials hanging off a B32.
 
The fault has been identified as warranting a C2.
No further investigation required.
Future fault finding with a view to correcting a fault is not the same thing as FI.
Valid point, and i see where you're coming from. ?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
bristol
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Open end to end on rn r2 - where should this go under in schedule of inspections?
Prefix
NAPIT Certification Scheme 
Forum
Certification NICEIC, NAPIT, Stroma, BECSA Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
sid521,
Last reply from
timhoward,
Replies
11
Views
3,645

Advert

Back
Top