If the output curve won't go above 3600 or thereabouts then your inverter is holding back the panels. As I understand it PVI-3.6-OUTD-UK inverters with a serial number greater than 621395 are affected this way.

If you ask to have a 4.2 fitted your installer may need to apply under G59 rather than G83. No harm in asking I suppose.
 
My Aurora has a much larger serial number wk 47 2011.
I think I'll monitor the situation for a while as it's not often up at 3.6kW at the moment. Hoping for sunny days ahead! I guess when the sun is not at the strongest then I'm still getting the benefit of having a larger system installed, and that is most of the time.
 
We aren't quite getting into the right time of year for peak outputs of your panels so I would hold back until it is definitely clear that the inverter is restricting output, I am sure these are clamped at 16amps which depending on your grid voltage could be anywhere around 3680w to 4000W. If you did want to go down the G59 route then you may be able to update the firmware on the inverter via a registered installer so that the 16amp limitation is removed, to be honest I don't think that overall you would notice a worthy increase in annual yield to justify the hassle.
You have to remember that these inverters were brought out specifically for the UK market to allow installers to comply with G83 recommendations and so there will be a slight compromise to reach that as was so with fitting the larger sma inverters and restricting outputs to 16 amps. In my opinion they are really good bits of kit and will easily complement a 4kw system especially if you are dual aspect or have strange shading issues!
 
  • Like
Reactions: 1 person
Unfortunately the recent versions post the serial number mentioned above are clamped at 16 amps or 3600 watts - whichever is LOWER. Strikes me as a very conservative reading of the G83 spec.
 
Hi, I have a Aurora PVI-3.6-OUTD-UK and mine also only goes to 3608 watts, but the real annoyance is that I have mine on two strings one string (A) with 12 panels (3Kw) and one (B) with 4 panels(1Kw).
The 1Kw string regularly hits 1230 watts DC when my irradiance meter registers .97, with string (A) disconnected, the other string 3Kw hits 3390 watts, when string (B) is disconnected, so adding both together it should be possible to achieve 4Kw regularly.
Below is a row from the Aurora data logger with both strings connected Yellow is DC String (A) and Green is DC String (B) red is AC output, sadly I didn’t log grid voltage but this is still useful info.
This shows String (A) generating 2503.04 watts DC and String (B) generating 1255.11 watts DC.

14:23;2;PVI-3.3-OUTD-UK;D;391.1;6.4;2487.7;117.3;10.7;1231.0;3607.4;

With string (B) disconnected this is the results

14:26;2;PVI-3.3-OUTD-UK;D;406.7;8.3;3368.6;0.0;0.0;0.0;3266.4;

The reason I chose this inverter was because the tech spec (http://www.power-one.com/renewable-energy/products/solar/string-inverters/aurora-uno/pvi-30-pvi-36-pvi-42/series) clearly states it will peak at 4000watts (230VAC – 17.2 Amp) well it don’t.
My next step is to see if I can get my money back and replace with SMA 5000TL because I give up with Power One.
 
I share your frustration - I have a 3.91 kWp scheme and when the sun is out the output is regularly limited to 3.6kw. This is due to the type of connection, G83, which specifies what generation you can connect to the mains. To get more output than 16A you would need a G59 connection agreement. I understand that these can take some time to obtain and I guess may cost money to get, unlike the G83 which is essentially plug and play from the installers.

I have decided not to pursue it and accept that I am capped when the a) the sun is out and b) when directly overhead. Most of the time I am not capped.

Let us know how you get on if you decide to change your inverter and by definition your connection agreements....


Hi, I have a Aurora PVI-3.6-OUTD-UK and mine also only goes to 3608 watts, but the real annoyance is that I have mine on two strings one string (A) with 12 panels (3Kw) and one (B) with 4 panels(1Kw).
The 1Kw string regularly hits 1230 watts DC when my irradiance meter registers .97, with string (A) disconnected, the other string 3Kw hits 3390 watts, when string (B) is disconnected, so adding both together it should be possible to achieve 4Kw regularly.
Below is a row from the Aurora data logger with both strings connected Yellow is DC String (A) and Green is DC String (B) red is AC output, sadly I didn’t log grid voltage but this is still useful info.
This shows String (A) generating 2503.04 watts DC and String (B) generating 1255.11 watts DC.

14:23;2;PVI-3.3-OUTD-UK;D;391.1;6.4;2487.7;117.3;10.7;1231.0;3607.4;

With string (B) disconnected this is the results

14:26;2;PVI-3.3-OUTD-UK;D;406.7;8.3;3368.6;0.0;0.0;0.0;3266.4;

The reason I chose this inverter was because the tech spec (http://www.power-one.com/renewable-energy/products/solar/string-inverters/aurora-uno/pvi-30-pvi-36-pvi-42/series) clearly states it will peak at 4000watts (230VAC – 17.2 Amp) well it don’t.
My next step is to see if I can get my money back and replace with SMA 5000TL because I give up with Power One.
 
Hi, Yes just ordred a SMA Sunny Boy 4000TL its still G83, if it don`t get to 4Kw guy said he would change to 5000TL at no extra cost he was so confident 4000TL would be ok.

I,ll let you know.
 
I'm lead to believe it's how the 4000TL is set-up initially. If you're G83 then it should be set to G83 and be capped to a 16A output, if you're G59 then it's not capped.
 
Yes, you are correct,just had a chat,he thought I was G59 and I`m not so all cancelled and back to squre one !
 
Sizing an inverter is quite complex to get it correct, if you have an inverter that is too large, IE a 5000TL on a 4KWP system, of course it should never "max out", however, it takes more power to run a larger inverter also its start up voltage is normally higher, so it may well produce less KWH's per year.

Because the weather is not constant, we do get peak days, and peak times of the day also, therefore if an inverter peaks on the odd occasion, it will probably be working at it's optimum (sweet spot) most of the time, so over a full year producing you more KWH's.
 
Hi Guys, I have a SMA 3600tl-20 and have seen my output peak at 3685w and never higher. ANyway, out of interest I just logged in as an installer on my Sunny Explorer and saw I could change the output from 3680 to 3740w so I did just to see what happens? Well, the inverter turned off and then came back on. Anyway, its not sunny at the moment but do you think I will see the peak output go up to 3740w now or should I change it back?
 
Your inverter is set at 3685w to be compliant with the G83 rules, so by changing it you really should have G59 approval from the DNO.
G83 means as it is limited, an installer can fit a system then tell the DNO that it has been installed, over 3680w or 16A you need to have approval from the DNO first, which they may insist on some upgrades.

I do except that it is only a little over, but it is still over, also you may find that it trips out, doubtful, but possible.

I hope this helps.
 
Last edited by a moderator:
I am indeed: Hampshire, 40 deg roof, 10 degrees east of due south.

Happy to wait a bit but the consistent peak value did make me think there was a ceiling somewhere. I've now gone back and looked at the inverter log files and the DC peak wattage from the panels appears to be roughly 3700 watts so perhaps it all makes sense for the time of year.

I have seen the Aurora PVI-3.6-OUTD peak slightly above 3800W on many occasions and different installations you will have losses through your Inverter plus the power ratings of your panels can be slightly higher or less than what they are rated at plus you have losses through your dc cables too. This is with GS83 settings too
 
Hi Guys, I have a SMA 3600tl-20 and have seen my output peak at 3685w and never higher. ANyway, out of interest I just logged in as an installer on my Sunny Explorer and saw I could change the output from 3680 to 3740w so I did just to see what happens? Well, the inverter turned off and then came back on. Anyway, its not sunny at the moment but do you think I will see the peak output go up to 3740w now or should I change it back?
this is why we change the installer password. Not that 60 watts is going to make any difference, but we've put our names to the fact that the inverter is limited to 3680W, but it's not really if the customer can just log in and change it themselves.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
peak real-world output of Power One Aurora PVI-3.6-OUTD-UK
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
35

Thread Tags

Advert

Thread statistics

Created
Sunshine777,
Last reply from
Gavin A,
Replies
35
Views
10,834

Advert