hi im an industrial electrician and have a small question about connections, im planning to put some juntion boxes above the ceiling in the kitchen as the the kitchen ring was part of the ring for the rest of the house and i now want to take all sockets in kitchen out of this ring and give the kitchen its own ring.
My question is,is putting j/b in the ceiling ok if i use inline crimps with a calibrated crimper, would this be thought of as a permanent connection?

many thanks

Nick
 
No probs with that method.

However, any work in a special location (kitchen, bathroom garden etc), or any new circuits will need to be notified under Part P of the building regs.
 
hi im an industrial electrician and have a small question about connections, im planning to put some juntion boxes above the ceiling in the kitchen as the the kitchen ring was part of the ring for the rest of the house and i now want to take all sockets in kitchen out of this ring and give the kitchen its own ring.
My question is,is putting j/b in the ceiling ok if i use inline crimps with a calibrated crimper, would this be thought of as a permanent connection?

I've started using Ashley j/b's that have maintenance free connections, only downside is there expensive.
 
Hey bud.

I havn't tried the ashley ones myself so would be interested to hear opinions.

I have tried the WAGOBOX ones and personally thought they were terrible.
 
No probs with that method.

However, any work in a special location (kitchen, bathroom garden etc), or any new circuits will need to be notified under Part P of the building regs.

What do you mean by "notified under Part P of the building regs?

Im after putting some outside lights in my garden but im not sure about the whole part p certifications as i work in the Industrial sector

Thanks for any help!
 
What do you mean by "notified under Part P of the building regs?

Im after putting some outside lights in my garden but im not sure about the whole part p certifications as i work in the Industrial sector

Thanks for any help!

As i understand it - a new circuit going outside would need an EIC certificate either from a member of a certified persons scheme ie member of niceic, elecsa or napit, or you would need to inform your local authority building control who would want to come out and look at it. It would have to be rcd protected.
Not sure what the case is if you go for a transformer and extra low voltage, though suspect it is just the same.
 
Ashley box's are good but as said expensive at the moment.
I use the cheaper option of a 77p chock box from toolstation & use crimps instead of terminal strip. Quick easy & cheap.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
permanent connections
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
bagnall007,
Last reply from
not clever,
Replies
8
Views
1,951

Advert

Back
Top