Have to agree with "Engineer", you can never have too many earths!

Sure you got those numbers the right way round Telectrix?

if i calculated right, 2.8mV/A/m. VD of 6.5V @3%. 11.5V @ 5%. ( the 6.5 should be 6.9V though, which will allow for 33A)
 
Apology Telectrix, your right, Im wrong --- I didnt read the question correctly! Luckily my exam days are over ........
 
If you saw my garden you would see why 75m is rather big to me, agreed though, I have a friend with 2 acres and that's more a field than anything. Should I not be working it out on 2.4mV/A/m not 2.8mV/A/m if I am using 3 core though? Its going to have a 6A light circuit on the end a 32A ring, so at most if I said 38A max demand worst case, gives me 6.8v drop which is fine as he will never use that much unless he intends on growing something down there. I agree though, PME and an extra rod is not too different really as you say.
 
the 2.4 figure is for 3/4/ core 3 phase. for single phase, you use the 2 core column in the OSG table as the cpc core is irrelevant for the purpose of calculating VD.
 