PeterJLavery
On point A) though with 2.3 ohms being a 100 amp fault current which depending on the type of breaker B,C,D and current carrying capacity of the rcbo then hoping that 100amps is enough to cause a thermal cutout due to excessive heat, and a 100amp fault current is more than enough for an unbalanced magnetic force also tripping it out? Would it be due to thermal cut out and not from RCD