Quick query I’m hoping someone can clear up. Im just looking at an example of a schedule of test results in a book I’m studying and I’ve come across an example I don’t understand. A lighting circuit protected by a 6amp 60898 Type C (Ref Method 100) using 1.5/1.0 T&E is measuring out R1+R2 at 0.12. The circuit is approx 38 metres in length.

Working off the calculation that the R1+R2 should be around 30.20 ohms x 38 / 1000 = 1.14. I can’t understand how they have reached this figure. There may be a shaver socket on the circuit as it mentions one of the circuits does have a shaver socket (but it doesn’t specify which), but I don’t know if that would impact anything? It could just be the test reading has been mis-typed but it would be great to get to the bottom of it by learning something new. Just wondering if it’s anything obvious to the vast sea of experienced helpful heads out there.

Thanks again.
 
What is the book and in what context are you studying it?

I believe R1+R2 for a 1.5/1.0 cable is 0.03 ohms per metre which would make it 1.14. This suggests it is a typo in the book.
 
What is the book and in what context are you studying it?

I believe R1+R2 for a 1.5/1.0 cable is 0.03 ohms per metre which would make it 1.14. This suggests it is a typo in the book.
1.14 @ 20 deg. C, so probably 1.2 @operating temperature. typo.
 
Geez, thanks guys, good to get your advice. The book is Practical Guide to Inspection, Testing & Certification of Electrical Installations (18th ed.) by Christopher Kitcher.

These books can cause more questions than give answers when they contain errors like that. It's a bit annoying sometimes for someone trying to learn. Thank god for forums like this.

IMG_1433.JPG

IMG_1434.JPG
 
Not sure I like that picture of the IR test on that TP&N board.
That RCBO is still energised and Neutral has not been linked to the phases.
 
Also goes onto show that the Zs is incorrect too. He has just added the 0.63 Zdb reading to the R1 + R2 therefore extending the error across too lol. Look at the relationship between Zdb, R1+R2 and Zs's. They never work quite like that when measured. Goes to show why you should always really take a Zs!! Maybe Chris Kitchener threw that in there to see if you'd notice......NOT haha. Anyway, we'll done OP, you are a sharper student than many that you noticed it. Good on you mate!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester

Thread Information

Title
Rather Low R1+R2 Query
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
11

Thread Tags

Advert

Thread statistics

Created
junksamiad,
Last reply from
TJ Anderson,
Replies
11
Views
2,224

Advert

Back
Top