My turn to ask a question ,
Why would earthing issues affect the trip time of a rcd ?
Why would earthing issues affect the trip time of a rcd ?
Surely if you test at the CU you will get a perfect reading every time?
If you test at the end of the circuit you will ensure a) the earth is continuous and b)the EFLI is low enough to operate the device in the required time.
Am not sure why you would want to ensure that the RCBO is fine, whilst the circuit and accessories that the device is meant to protect may harbour a fault that causes the (perfectly fine) RCBO not to operate in the required time?
I am not trying to be confrontational, I am simply confused as this is the first time I have encountered this method of recording trip times. I always record from the end of line.......
^^^which is what i've been trying to explain for the last half hour lol.
I have to agree with biff on the above.
RCD test should be done with loads disconnected and a EFLI test prior to RCD testing.
As mentioned the times can be alot different if equipment is left connected.
GN 3 Rcd testing also makes mention of this.
It's just clicked, the test meter sends a 'pulse' to initiate the trip. Ballast/transformers/loads can absorb some of this 'pulse' and give spurious readings.
I think...

Whilst each line has provision for RCD times you only have to record the times on the line the RCD itself is on, unless you're saying that you don't actually have RCD's on their own line?However, the NICEIC forms I fill in have a seperate box for the RCD disconnection times for every circuit. So when I fill these forms in, I measure the RCD connection times for each circuit, and record them appropriately