A simple one I guess but one I have not come across:

3 bed house - 1 CU - 16th edition I guess with 1 RCD covering 5 circuits.

The kitchen was on the downstairs ring.

I have added a brand new kitchen ring and a 6mm cooker feed.

Can I use RCBOs to protect the circuits on the spare side that is currently unprotected by the rcd?

Thanks All
 
I did the same in my kitchen but that was before part p. It was perfectly ok then. Now ? Not sure, the part p guys will tell you more.
 
Absolutely fine
 
Yes but you only need to on the circuits you have installed or extended. Depending on the board RCBOs can be a very tight fit due to the height and can be very tight against the earth and neutral bars making a tidy job almost impossible.
 
I think you need to confirm this as it'll impact what you can do!

Defo 5 circuits that cover the RCD - meant (I guess 16th edition install).

- - - Updated - - -

Board is a Wylex - (£100 screwfix jobby) - what are the RCBO fit in these like?
 
Fitting RCBOs in a Wylex NH CU is usually pretty straight forward from memory, about 50mm headroom above the RCBO, not the best, but far from the worst CU on the market.
 
A simple one I guess but one I have not come across:

3 bed house - 1 CU - 16th edition I guess with 1 RCD covering 5 circuits.

The kitchen was on the downstairs ring.

I have added a brand new kitchen ring and a 6mm cooker feed.

Can I use RCBOs to protect the circuits on the spare side that is currently unprotected by the rcd?

Thanks All

If you have calculated your maximum demand and the installation allows then the suggestion you put forward is the most desirable in my opinion.

You may or may not be aware that the work you mention is covered under Part P of the Building Regulations therefore it will need signing off appropriately.

Only once have I struggled with Wylex RCBO's and that's only because the installer before had thrown in the cables and left very little room. after a few alterations they slotted in just fine and the new cables terminated perfectly.

:thumbsup
 

Reply to RCBO Question in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock