Is it a split load board with one rcd and a couple of rcbo's ?
cowboys like you keep me in a job......
I am a good ----- cat, i will not say anything, i won't, i won't, OK i will TRY not to say anything!Gods sake, use an insulation resistance tester, trace where it's down and correct it, then alter board to make it 17 th compliant complete the paperwork and notify your partp body of the work.
Many thanks nick and others i,ll go back and retest and check for crossed and shared neutrals as you suggest and use my Di-log leakage current tester for checking the highest earth leakage