I Need a little help i recently fitted a new consumer unit for a mate. The house is empty and up for sale so i thought no problem as not in a hurry continuity was ok on all circuits IR ok ,Ze 0.09,PFC 2.95kA so i changed the board then powered up and the 80a 30Ma RCD tripped i disconnected each circuit and reset it tripped on each circuit. I've since gone back with a clamp meter and found 29-39Ma running through the bonding. I clamped ( on lowest setting)the neutral and line seperately on each circuit and got kitchen N-0.70 L-0.46Ma and downstairs lights N-0.47 L 0.10 surely these differences in reads are too high can anybody steer me in the right direction. :frown2:
 
If you say it tripped out on each circuit (mcb) then it looks like a neutral fault.

Disconnect all neutrals and do IR again. If it is a 17th edition board with 2 RCD's make sure you have not got neutrals crossed between RCD's. Finally check if upstairs lighting has a "borrowed" neutral ie. The landing light has not got its neutral from downstairs lighting circuit.
 
If you say it tripped out on each circuit (mcb) then it looks like a neutral fault.

Disconnect all neutrals and do IR again. If it is a 17th edition board with 2 RCD's make sure you have not got neutrals crossed between RCD's. Finally check if upstairs lighting has a "borrowed" neutral ie. The landing light has not got its neutral from downstairs lighting circuit.

Correction meant to say upstairs!
 
it's an 8 way BG board with only one 80a 30Ma RCD the readings are taken from clamping each circuits line and neutral as the RCD keeps tripping MCBs are fine what do you make of the 29-39 Ma current going through the bonding ?
 
it's an 8 way BG board with only one 80a 30Ma RCD the readings are taken from clamping each circuits line and neutral as the RCD keeps tripping MCBs are fine what do you make of the 29-39 Ma current going through the bonding ?

So it's not a 17th edition board, i think you only have a clip on Amp meter, are you an electrician?
 
hmm its a British General 17th edition Board a digitron clamp meter and im 17th edition mr cat

I don't see how it is 17th edition with only 1 RCD.

Yes you have a clamp meter, good for you. You have not said whether it is your only meter.

Do you have an IR meter.

You did not answer whether you are an electrician or not.

Thank you Mr Gary
 
New posts

Reply to RCD Earth Leakage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
378
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock