D
domn
one thing to check is that you have not put your meter onto test a dc rcd i was having the same thing on a job took me bloody ages to realize.
dom
dom
Onions, thanks for that, that was what I was thinking, i was beginning to think I had missed something. But as the r1 and r2 and insulation tests are ok there shouldn't be a damage to the cable. I checked all connections were tight in both the shower and the switch unit.
You have not mentioned ZS! I take it your shower unit has a ZE /Ra ?Hi, I've been installing a new shower, using a shower consumer unit complete with rcd. All the tests passed, r1 And r2 were 0.23 ohms, insulation resistance was >299M ohms, polarity was correct. But when I test the rcd I cannot get it to trip. It passes when the test button is pressed but will not pass the rcd test at 1 or 5 times, it fails to trip and my tester says time exceeded and shuts off.
Every thing appears correct I ran out of time so have isolated it the shower and will investigate it again tomorrow.
all advice would be appreciated.
thanks
Hawk moon, I will try your suggestion tomorrow, I've got to prove rcd, either is duff or that there a fault elsewhere.
Thanks to everyone for all the advice, as always it's helpful.
You mean what I suggested in post 9?