hi guys and girls,
I'm new to the forum,
recently left the army and did a short electrical course. (doesn't make me an expert by no means)

my problem is this:

my sister has just bought a house and as a favour I said I would sort her electrics. The house is old (bout 1930s) had old style MCBs I replaced the fuseboard to a split load board (2 RCDs) and wired it upup. Chuffed with myself I tested all the circuits, (end to end, continuity etc...) working fine turned on the power and tested the downstairs sockets. the rcd trips every time a load is put the circuit. upstairs works fine (waiting for lights so not got to them yet) kitchen not done yet. just upstairs sockets and frontroom are done except for this.

any help please guys and girls

Hello and welcome to the forums.

Ok if you have a half decent tester, and GN3 then you will be able to carry out your tests. As you have said, you tested them all. Could you list your schedule of test results, then we can look at them as a starting point,going forward.

Cheers
Toony
 
Hi mate if you had tested before changing the board you would have identified that the wiring did not comply and would possibly need rewiring or rectifying
as you say the IR readings were less than 1.0M/Ohm this indicates a latent defect I.e poor insualtion of the conductors this could be due to a mumber of factors such as age, overloading, Mice etc etc
any reading below 1.0M/Ohm is a fail on the Insulation resistance test results so does not comply with BS7671

was this a global IR test if so test the circuits individually to find if 1 or all are defective if you have already then its a fail and requires rectifying all circuits as you say its from 1930s its already beyond its reasonable expected working life and should ideally have all been rewired anyway

was the cable lead sheathed or VIR
 
PAT test what you're plugging in.

Could just be a faulty appliance...

Thats my contribution anyway as everything else has been covered.
 
Hi mate if you had tested before changing the board you would have identified that the wiring did not comply and would possibly need rewiring or rectifying
as you say the IR readings were less than 1.0M/Ohm this indicates a latent defect I.e poor insualtion of the conductors this could be due to a mumber of factors such as age, overloading, Mice etc etc
any reading below 1.0M/Ohm is a fail on the Insulation resistance test results so does not comply with BS7671

was this a global IR test if so test the circuits individually to find if 1 or all are defective if you have already then its a fail and requires rectifying all circuits as you say its from 1930s its already beyond its reasonable expected working life and should ideally have all been rewired anyway

was the cable lead sheathed or VIR
yeah...i`v got a part rewire on a house coming up....its been fire damaged on the ground floor.....theres a new board going in as well...once all the damaged cable has been removed the rest will get zapped to verify its still good.....
any crap/low readings will be dealt with beforehand...
will be going back tomorrow to speak to the occupiers as to new points etc....
perfect time to get a pre-remedial Ze...
 
hi guys and girls,
I'm new to the forum,
recently left the army and did a short electrical course. (doesn't make me an expert by no means)

my problem is this:

my sister has just bought a house and as a favour I said I would sort her electrics. The house is old (bout 1930s) had old style MCBs I replaced the fuseboard to a split load board (2 RCDs) and wired it upup. Chuffed with myself I tested all the circuits, (end to end, continuity etc...) working fine turned on the power and tested the downstairs sockets. the rcd trips every time a load is put the circuit. upstairs works fine (waiting for lights so not got to them yet) kitchen not done yet. just upstairs sockets and frontroom are done except for this.

any help please guys and girls

Unless it has changed in the new version of Part P have you informed the LABC about changing the consumer unit?
 
Hi guys quick update.

Re did my IR all came back as >500M ohms
reduced to intermittent tripping of the rcd!!

Any ideas?
 
i would recommend dismantle and engage one by one but it could be crossed neutrals on rcds meaning you have one on one rcd but a interconnection is on the other generally found in two switching with strappers instead of 3 core?
 