Have a job where the customer has nuisance tripping of the 30mA RCD (Don't you just love these jobs!)
Tried to complete a 1x and 5x test on the RCD-fails test >300ms and >40ms respectively
Changed RCD but still have the same problem
RCD tested at DB
TNS system but measured Ze is 66ohms. DNO contacted to investigate high earth reading.
But why is the RCD test causing me problems?
Shouldn't the RCD still pass the test even with a high Ze reading?