Have a job where the customer has nuisance tripping of the 30mA RCD (Don't you just love these jobs!)

Tried to complete a 1x and 5x test on the RCD-fails test >300ms and >40ms respectively

Changed RCD but still have the same problem

RCD tested at DB

TNS system but measured Ze is 66ohms. DNO contacted to investigate high earth reading.

But why is the RCD test causing me problems?

Shouldn't the RCD still pass the test even with a high Ze reading?
 
Did you try testing the RCD away from the board? If not, be aware that some RCDs won't work when tested by probing the terminal screws, but only if the test current passes through the proper cable entry ports on the RCD. You can do this either by testing on the final circuit itself, or by connecting in a couple of short temporary wires and connecting your tester to the ends.

Edit: If it's an RCD rather than an RCBO you can test at the RCD-protected outgoing busbars.
 
I ha one recently where a neutral to earth fault led to simillar symptoms, RCD not tripping on test button or proper test, RCD holds fine until a certain amount of load is added, adding load to non RCD circuits causes RCD to trip.
Very puzzling at first but when you think about it for a second you realise the neutral to earth fault acts a resistance in parallel with the normal neutral.
As the fault had a couple of ohms resistance there had to be enough load applied to result in more than 30mA imbalance across the RCD.
 
it`s a neutral-earth fault is this...
drop each circuit out in turn being fed through that RCD...
IR testing...
 
RCD not tripping on test button or proper test
The RCD is faulty - if the wiring is correct

RCD holds fine until a certain amount of load is added, adding load to non RCD circuits causes RCD to trip
That's not possible - if the wiring is correct.

Very puzzling at first but when you think about it for a second you realise the neutral to earth fault acts a resistance in parallel with the normal neutral.
No, it doesn't. It just provides a shared path with the neutral but if it is not on the RCD side it will not trip it - if the wiring is correct.

As the fault had a couple of ohms resistance there had to be enough load applied to result in more than 30mA imbalance across the RCD.
It doesn't work like that.



Wiring not correct somewhere.
 
I wish I was psychic like you and could see all this without going there!

Swapped the two RCDs in the board to prove RCD working correctly.

That is possible, I watched it happen.

Shared path / parallel path its the same thing with a different name. The L-N loop was 0.25ohms the fault was 1.02 ohms steady between N and E added to Ze of 0.25ohms (PME) gives a return path of 1.27 ohms through the fault.
Current will divide proportionally between the normal neutral return path and through a return path through the fault to earth and then on to incoming neutral via the cpc/earthing conductor/pme connection.
The neutral current from the other side of the board will travel through its own RCD as per normal and split between the parallel return paths at the point where the main neutral splits to the RCDs.
This is exactly what causes an RCD to trip if you touch N and E together on a dead circuit, part of the neutral current in the installation flows to earth and causes said imbalance.

Yes RCDs do work like that, they operate on an imbalance of current flowing through live and neutral.
 
i've had that type of fault as well. a N-E fault on 1 RCD side causing the other RCD to fail on test. took me 2 hours to find it. turned out to be damp in a FCU for toilet fan. tracking across the FCU terminals.
 
Shared path / parallel path its the same thing with a different name. The L-N loop was 0.25ohms the fault was 1.02 ohms steady between N and E added to Ze of 0.25ohms (PME) gives a return path of 1.27 ohms through the fault.


Maths aside - but that current (on unprotected side) is not going through the RCD.

If you disconnected the neutral from the board then you would have up to (240/1.02) 235A through the fault.
That will soon clear it.

Current will divide proportionally between the normal neutral return path and through a return path through the fault to earth and then on to incoming neutral via the cpc/earthing conductor/pme connection.
But not through the RCD.

The neutral current from the other side of the board will travel through its own RCD as per normal and split between the parallel return paths at the point where the main neutral splits to the RCDs.
Your original post talked of a fault on non-protected side.

This is exactly what causes an RCD to trip if you touch N and E together on a dead circuit, part of the neutral current in the installation flows to earth and causes said imbalance.
But only on the circuits protected by the RCD.

By that logic, ALL RCBOs would trip with one fault (or one touched N and E) anywhere.

Yes RCDs do work like that, they operate on an imbalance of current flowing through live and neutral.
Yes but only on the circuits protected by that RCD.
 
I can understand why the E-N fault causes the RCD to trip when I do a Ze test. But can't understand why the RCD fails the 1x 5x test. Struggling to get my head around that one!
 
I said load on the non rcd side not that the fault was on the non RCD side.

The fault is on the RCD side, Load on the non RCD side results in the neutral current dividing through the parallel path of teh fault which means the current is effectively backfeeding through the RCD this is what causes the RCD to operate.

By this logic not all RCBO's would trip, I am talking about the diverted neutral current going through the RCD the wrong way and then through the fault. RCBO's would mimic this behaviour if their was similar fault on the outgoing side of one of them.

Jeezus will you learn to read properly and take the time to think and learn the science before spouting off your ****!

You are more than welcome to meet me on site tomorrow when I go back to fix this and witness this happening for yourself.
 