Having a bit of a brain freeze moment.

I have a 2-core SWA cable running to an outbuilding. The sheath is used to earth this cable back to the consumer unit in the house which is TNC-S, while the outbuilding has its own earth electrode (ie it's TT) protecting its Consumer Unit. That's to say I've not exported to PME to the outbuilding as it's a long way from the main building. The SWA cable is thus protected from someone putting a shovel through it by the RCD in the main building (It's a single RCD which protects all the circuits).

All well and good, but, and don't ask, I've totally blanked how to test the RCD in the house to ensure a fault with the SWA cable will trip it. As I recall I just energise the MCB covering the SWA, connect my earth lead to the disconnected earth conductor which is connected to the sheath of the SWA cable and then the line lead to the top of the RCD (Line) and do the test, repeating for the neutral.

I know I don't have to do this as such, I could just test the RCD from anywhere in the main house for the paperwork, but it's for piece of mind really that everything connecting the house to the outbuilding has been done right, and it will trip the RCD in the main house under fault conditions of the SWA.
 
Would you not be better to omit the house rcd for the swa and use local rcd or RCBO’s for the outhouse circuits?
or even a 100mA unit if you can’t achieve discontinue times without.

and yes, to test rcd you could just attach leads to incoming supply to outhouse consumer unit.
 

Reply to RCD Test of SWA Cable in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
705
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock