and the fault was......??????
Causes of neutral to earth fault? Most possible cause rat bitting


he must live in a rough areainfested with rats
Neutral to Earth fault (short circuit) plastic outer cover bitten and damaged, short circuiting the Neutral to Earth. The RCD trips (even if you keep all the MCBs off). No way to get power back .. either you find the fault and repair it or bypass the RCD (not recommended)and the fault was......??????

yep -never bypass an rcd
N-E fault usually trips rcd when you plug in a class2 appliance on a protected circuit
it trips with the mcb off because you have zero current flowing in the line. anneutral/earth fault wilcause current to flow throgh the neutral to earth, thus causing inbalance. with class 2 equipment, the earth is not connected to the appiance, so no fault current. sssssssimple.