Appliance still plugged in. Cooker hood, FCU will be behind chimney.
Even turned off at socket, can still get an N-E fault to trip rcd.
Have you checked the mcb isn’t at fault?

Buy yourself a notepad and a pencil. For taking notes.
 
Is the heating fed by one of these circuits? If the RCD trips yet you've got good IR readings that implies an intermittent fault which can be caused by e.g. the heating/water heating coming on and there's a faulty component (pump, valve, boiler pcb, immersion element), or a compressor motor kicking in.

A healthy ring circuit has a natural earth leakage of about 3mA, the power supplies for modern equipment such as TVs, PCs, phone chargers etc also have quite high earth leakage; when it trips it could it be the sum of these exceeding 30mA.

Does it trip when you're there and have disconnected everything, or when stuffs plugged in/switched on?

Is there e.g. a PIR external light fed via a FCU on the circuit?
 