been living in this house for 8years after it was fully re-wired, today the kitchen plugs trip the RCD when any power is drawn (apart from the cooker CLOCK), all the appliances are fine, any socket that I use trips the RCD, any ideas
Might be an idea to get some testing done Mate
Unplug all appliances, not just turned off at the wall.
An rcd detects neutral to earth fault as well as live to earth.
Any dampness in the rooms?
Recent work done?
Signs of rodents?
can be a N-E fault, not necessarily on the circuit that seem to trip the RCD, soon as any sort of load is applied, boompf. some serious testing needs to be carried out,
Yup, sounds like N--E fault. Likely to be the kitchen circuit or an appliance plugged into it although not 100% guaranteed to be unless it has its own RCD. N-E faults that trip on load will be on a circuit protected by the RCD that trips, but not necessarily the circuit on which you are applying load to make it trip.
Reply to RCD tripping out on plug circuit in the UK Electrical Forum area at ElectriciansForums.net
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...