been living in this house for 8years after it was fully re-wired, today the kitchen plugs trip the RCD when any power is drawn (apart from the cooker CLOCK), all the appliances are fine, any socket that I use trips the RCD, any ideas
 
been living in this house for 8years after it was fully re-wired, today the kitchen plugs trip the RCD when any power is drawn (apart from the cooker CLOCK), all the appliances are fine, any socket that I use trips the RCD, any ideas
Might be an idea to get some testing done Mate
 
Unplug all appliances, not just turned off at the wall.
An rcd detects neutral to earth fault as well as live to earth.

Any dampness in the rooms?
Recent work done?
Signs of rodents?
 
can be a N-E fault, not necessarily on the circuit that seem to trip the RCD, soon as any sort of load is applied, boompf. some serious testing needs to be carried out,
 
Yup, sounds like N--E fault. Likely to be the kitchen circuit or an appliance plugged into it although not 100% guaranteed to be unless it has its own RCD. N-E faults that trip on load will be on a circuit protected by the RCD that trips, but not necessarily the circuit on which you are applying load to make it trip.
 

Reply to RCD tripping out on plug circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
762
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
758
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock