I posted a reply similar to this problem sometime ago. I would go with Spark 68 on this one. I had a similar problem, where you could turn the lights on, but as soon as you plugged in an appliance the Board RCD tripped. The fault was that the internal 'tails' within the CU had been connected incorrectly. Worth a check,

Regards.
 
EFLI tested at 1 socket tripped RCD, but was ok at another,this socket also gave me a higher R1+R2 than others but was fine at terminals on back of socket so I changed the socket but didnt check ZS at this socket afterwards, by this time by head was begining to hurt.

as the other guys are saying the RCD checks what is going in thro the phase and back via the neutral. if you are not getting the same in and out the tordiol inside the RCD senses an imbalance and trips. check that all the neutrals and earths are in the correct place. if you have any transformers in any of the circuits check that they are not faulty. as the neutrals and earths end up at the same place it has got to be on the return/neutral side that you have a fault other wise you would have a dead short.

good luck finding your needle in a haystack!
 
my money's on a N fault. wrong N bar in CU, loose N on supply side. etc.
 