As we seem to be in the mood to endlessly debate this now-fixed case, lets move on to the issues with the case of (A) and why it would not be acceptable.(A) has lots of potential for issues, (B) does not, and therefore (A) does not comply with the regs
Excellent thread! Ordinarily by post #122 I'd have a long list in my mind of various points not yet addressed or imperfectly answered and still apparently worth tackling. Here, there's little I can add.
Although, one point that I can't recall being drawn attention to explicitly is to limit the scrutiny of the bow-tie circuit to the cable configuration. Consider a normal ring that is fully compliant in every way, that is rewired into a bow-tie. The only thing that has changed is the wiring layout; the number of points, total load, the area served and subdivision of the load into separate circuits have not changed. Comparing these two situations is the heart of the matter.
Clearly, if a situation requires two separate circuits or >32A, and yet is served by one 32A bow-tie circuit, it's inadequate, but a conventional single ring would be inadequate in the same way. This does potentially apply in the OP's scenario because there is evidence that the installation was originally two circuits totalling 64A OCPD, therefore it is likely that the present bow-tie is inadequate for reasons other than the way it's connected. Such problems could be equally important for both safety and compliance reasons, but they are not about bow-ties specifically.
The same is true for four conductors in a terminal - it could be a risk but it's not specific to bow-ties. One could imagine three conductors being securely clamped in a trefoil, and the fourth one not receiving its share of the force. Or, all four initially being clamped but not lying snugly side by side, so that thermal movement causes them to give into a slacker configuration. (I was pulled up by an NIC inspector for having put three cables into an MCB terminal!)
I agree that in operation, specifically, if the same points connected in a ring would be both safe and compliant, then the bow-tie will be equally safe or more so, due to the likely lower fault loop impedances at some points. However, during maintenance and testing I agree that it is a potential trap for the unwary that could reasonably be expected to result in confusion or incorrect methods being applied. It is a circuit layout that is not explicitly defined, cannot be simply tested by the method that is defined for RFCs, and does not compensate for these abnormalities by a significantly improved level of safety in some other way. That would make it a C3 IMHO.
There was another thread that brought up the "lollipop circuit" where something like an unused cooker feed has a kitchen ring final circuit added to it, and my issues with that were not the concept (as a garage CU with ring is much the same) but this issue of testability and documentation (or the likely lack of) to determine its existence and to have access to the ring ends for testing.And that's the crux of it. It's mostly about our inability to properly test it and thus our inability to be certain it's safe.
There was another thread that brought up the "lollipop circuit" where something like an unused cooker feed has a kitchen ring final circuit added to it, and my issues with that were not the concept (as a garage CU with ring is much the same) but this issue of testability and documentation (or the likely lack of) to determine its existence and to have access to the ring ends for testing.
@SparkyChick grading it as a C2 but equally it is not explicitly against any regulation that springs to mind (beyond good workmanship) and it is not "potentially dangerous" in the strict sense so it could easily be coded C3 as a result.
In software engineering there is something known as the "principle of least astonishment" which has it that anything behaving in an unexpected or unconventional manner is bad practice. We really need something equivalent in the wiring regulations:
Principle of least astonishment - Wikipedia
en.wikipedia.org
I think what this thread has thrown up is there really ought to be some regulation to cover issues of unconventional arrangements, inadequate documentation, or insufficienct access to cicuits junctions that present an issues for unexpected behaviour or inadequate fault coverage when testing.
Exactly!So, I don't particularly see testing a lollipop as the issue. I would say the documentation is the key, in particular making a note of where the transition point is so it can be accessed if required. Problems arise here if it's not a maintenance free junction box and it's say under the bathroom floor
A former colleague who is a software engineer told me about that one, I was astonished.Having been a software engineer for over 20 years, I must admit that's a new one on me.
If everyone was as competent and conscientious as you would not be debating this now! Thanks again for your detailed inputs.On the subject of documentation, I just look at it like this... if I got called out to one of my jobs, what information beyond the test results would help me and I generally stick whatever I think of on a generic continuation page and/or produce diagrams. I also try and think ahead a little during the install and maybe have designated areas for junction boxes (Typically Wagoboxes) and I record those.
Question I have is, is it ok to have x2 ring main circuits on one 32amp type B MCB??
If so does this meet the current regs.
TIA.
What makes having 4 conductors wired as two rings on one fuseway dangerous? I have not seen an answer. There isn`t one
Depending on the area (in square metres) extend the ring. Failing that then use a spare way and create another ring circuit.I'm not saying it's correct just saying what I've seen. That's why I've asked the question to make sure its correct.
[automerge]1588089613[/automerge]
Thanks for the advice it is much appreciated?
Probably don't have a spare way, that's why there are 2 RFCs crammed into one OCPD maybe?Depending on the area (in square metres) extend the ring. Failing that then use a spare way and create another ring circuit.
The short answer is electrically, if the rings comply in their own right with the regulations, they should be safe, but there are possibly implications with the installation not being split to minimise inconvenience and possibly danger from other factors (such as a loss of power to say life supporting equipment). It's unconventional and I don't think any of us would install like it, but certainly I would do it at a pinch to restore supply as a temporary measure.
This circuit might be described as a "butterfly" circuit.
Then settle for it being a final circuit which isn't a ring final circuit. Let's call it a double ring final circuit if you prefer. (Or call it a crap final circuit if you like - few will disagree.)Final circuit. A circuit connected directly to current-using equipment, or to a socket-outlet or socket-outlets or other
outlet points for the connection of such equipment.
Ring final circuit. A final circuit arranged in the form of a ring (not figure of eight) and connected to a single point of supply.
Well I called it a butterfly circuit, anybody can call it what they want, no problem. Just like the age old cooker circuit, modified cos cooker not needed so a ring produced from that point, some call that a "lolipop" circuit or a "lassoo" circuit (not implying a cowboy job I hope!). The butterfly or whatever you call it just like the lolipop can be a decent circuit designed using sound engineering judgement and be ok. The fact that they are not easily recognised as standard circuits does nothing to detract from that. It might confuse the unwary a little but you could ask "should they really be adding/modifying these circuits if they do not fully understand what they are doing?". Answer No, they could ask someone who does know though and there is no shame in that. There is no person who knows everything about everything.Then settle for it being a final circuit which isn't a ring final circuit. Let's call it a double ring final circuit if you prefer. (Or call it a crap final circuit if you like - few will disagree.)
I prefer to call them an abortion, work of the Devil.I would prefer to call them "Bow Tie" circuits sounds more sophisticated don't you know, can't get on with "lollipop" circuits sounds very childish, "Dragon fly" or a "Damselfly" at least they have four wings, can't think of a "Butterfly" with four wings.
hate to correct you there, but like bees, butterflies do have 4 wings.I would prefer to call them "Bow Tie" circuits sounds more sophisticated don't you know, can't get on with "lollipop" circuits sounds very childish, "Dragon fly" or a "Damselfly" at least they have four wings, can't think of a "Butterfly" with four wings.
I prefer to call them an abortion, work of the Devil.
Beginning to sound like Mumsnet.Am I on the right forum here?
The rear set of butterfly wings are not always smaller the orange sulphur for example have slightly larger rear wings.But the hind wings are much smaller and not considered a lifting wing, they are there to counter balance the movement of the front wings hence the erratic flight, but a Dragonfly can hover.
[automerge]1588351348[/automerge]
The Work of the Devil is Clingfilm or is that the Devil spawn.
I wasn't referring to all non-standard circuits as crap. I'm not hygely in favour of four conductors in a circuit breaker etc. though. So it was this particular arrangement which I was suggesting that many might consider to be crap.Well I called it a butterfly circuit, anybody can call it what they want, no problem. Just like the age old cooker circuit, modified cos cooker not needed so a ring produced from that point, some call that a "lolipop" circuit or a "lassoo" circuit (not implying a cowboy job I hope!). The butterfly or whatever you call it just like the lolipop can be a decent circuit designed using sound engineering judgement and be ok. The fact that they are not easily recognised as standard circuits does nothing to detract from that. It might confuse the unwary a little but you could ask "should they really be adding/modifying these circuits if they do not fully understand what they are doing?". Answer No, they could ask someone who does know though and there is no shame in that. There is no person who knows everything about everything.
I disagree about calling them crap circuits though.
Another example to consider is a radial circuit, be it lighting or power points. You might branch out at some point for instance 1 begats 2 begats 4 begats 8 etc etc, it is still a radial circuit, again with different topology but nonetheless sound (some call them "trees"), in fact you could start it off with two conductors (or more) at the CU and it`s still ok - might be a beggar to test though! - you`d have several ends for Zs. It is up to the designer if they want to create one circuit,
In my example No 2/ is actually better in terms of volt drop and R1 + R2 than example No1 is.
I wasn't referring to all non-standard circuits as crap. I'm not hygely in favour of four conductors in a circuit breaker etc. though. So it was this particular arrangement which I was suggesting that many might consider to be crap.
A ring supplied by a suitably sized radial feeder is something which I have absolutely no difficulty with, even though it is non-standard.
Easy, just the ring of that particular fault. Same as any circuit connected in your consumer unit.So like a dog with a bone I have been thinking about this. I can't quite get my head around EFLI test what route would the current take on such a circuit? If I took it at ring A say, would it go around ring B or just ring A and the substation?
The test would give the most onerous as the answer which should be the 65m ring part of the circuitEasy, just the ring of that particular fault. Same as any circuit connected in your consumer unit.
I never suggested that any of them were unsafe. In fact I specifically stated that the circuit in question was not unsafe unless there was an issue with the connections to the four conductors at the origin.Whatever you label them does not really matter, they are not crap circuits, they may be decent reliable circuits if undertaken properly. The only problem is they are not commonly listed. BS 7671 tells you what to comply with it does not tell you how to comply. So long as you use sound electrical design it complies and is safe. No less so than if you use a bog standard ring or radial.
I can give one example of a circuit that probably does not comply but is nonetheless safe :-
a bog standard ring final circuit B32A MCB with a spur of one twin socket at the origin of the ring i.e from the fuseway. Compliant Yes. Now disconnect the ring but leave the spur in place, so now its a twin socket on a 32a mcb. we would not like the look of it but removal of the ring has not rendered it unsafe has it?