I've been asked to do a surface mounted ring mains in a residential property, is it normal practice to leave the wires loose in the conduit or would you tie wrap them together or use something else? Thanks in advance from a newbee
 
Are you really running T & E or was that a miss post. Also if you haven't done it before wiring a ring final circuit in conduit takes a bit of thinking through as you need to get your return leg back, I assume through the same outgoing conduit.

A way was pull 1st leg into 1st socket, 2nd leg into 2nd socket, 1st then to 3rd, 2nd to 4th etc using the boxes as pull throughs
 
As it's a residential property I'm guessing he means mini trunking for the drops???, otherwise it'll be a bit of a job pulling through conduits.
 
unforunately its going to be the entire ring in conduit, customer doesn't want boards up!! not looking forward to it, may see if I can suggest using slightly bigger conduit
 
I know, glad its not my place.....landlord decorated before getting PIR may take a picture and pop it on the site
 
Why would you pull T & E cables though Conduit? What about heat dissapation? The BRB states that the capacity of Trunking/Conduit should not exceed 45%.
 
OSG and BRB state 45% space occupancy for heat discipation for single core cable which I agree with, however running 2.5mm thorugh conduit (2legs) will give a cable factor of 143 and I was planning to ussing 50x38mm conduit which has a factor of 767. So I suppose as my calculation is not strictly speaking correct, I thought around a 20% space occupancy for T&E would be fine....happy to be corrected
 
As I suspected......you are referring to square/oblong mini trunking with a base and lid, as opposed to solid round conduit (pipe).
 