Hi i am doing some college home work (which i am fine with) its to do with the sequence of tests and i have been looking in guidance note 3 and in 2.7.4 is the sequence of tests but can i ask who does "f" 'insulation resistance of non conducting walls and floors' i ave never heard of this before when would you do it?
 
This is a special protective measure of "non conducting Location" that provides fault protection by virtue of there being no conductive paths in the location and all potentially live parts (in the case of a fault) are separated.
In this case you would need to check that the walls, etc. were non conducting and this is when you would perform the described IR testing.

This is not a general means of protection and would be rarely used.
 
Hi i am doing some college home work (which i am fine with) its to do with the sequence of tests and i have been looking in guidance note 3 and in 2.7.4 is the sequence of tests but can i ask who does "f" 'insulation resistance of non conducting walls and floors' i ave never heard of this before when would you do it?

The most common test sequence is:

Continuity of protective conductors, including protective bonding conductors. (dead test)
Continuity of ring conductors. (dead test)
Insulation resistance.(dead test)
Polarity (usually confirmed during continuity test if done by R1+R2 method)(dead test)
Earth fault loop impedance.(live test)
Additonal protection (RCD testing)(live test)
Functional testing.(live test)

Cheers…………..Howard
 
There have been a few. But if i can remember 7 items in the correct order, then it isn't difficult. The Schedule of test results is laid out in the correct order almost, just ring continuity and continuity wrong way round. It is still a good prompt to use though.

Cheers………..Howard
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Baker1988

Arms
-
Joined
Location
Kingston Upon Hull
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
sequence of tests
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Thread Tags

Advert

Thread statistics

Created
Baker1988,
Last reply from
SirKit Breaker,
Replies
5
Views
8,422

Advert

Back
Top