I am reviewing a EICR for a property I am buying. The vendor has had the EICR done, but both the Cooker and Shower are on 40A 60898 B curve mcbs and the cable type is shown as 2.5mm2 type A install methord C. I suspect a clerical error but as it is in the vendor document pack what would you suggest? The cooker is a four ring built in electric hob. The shower is an electricaly heated shower rateing of which to be checked tomorrow.
All the circuit insulation measurements are 500M ohm which is a bit sus.
 
Last edited:
Go and verify it.
 
I don't see the 500 Meg ohm as being 'suss' why wouldn't it have been assuming this is just a reading to earth.
 
  • Like
Reactions: DPG and nicebutdim
I don't see the 500 Meg ohm as being 'suss' why wouldn't it have been assuming this is just a reading to earth.

I was guessing it seemed suss as >999 is the sort of reading a lot of people would expect when results are the same on all circuits. Stands to reason the tester measures a maximum of 500mΩ.
 
It is 500M for both L to N and L to E
 
At 500V this tester measures a maximum of 500mΩ, which seems quite reasonable at 500x the minimum acceptable measurement.

 
What's 'suss' about that?
For an EICR I would question whether they really disconnected all connections across line and neutral to achieve an L to E reading.
 
For an EICR I would question whether they really disconnected all connections across line and neutral to achieve an L to E reading.

From information provided by the OP, it looks as though the EICR raises a number of questions about exactly what 'testing' & 'inspection' took place.
 
my problem here is that there is a reading from a 2,5mm on a 32a breaker.... not ok sorry just re read 40a breaker definately not ok
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

UKMeterman

Arms
~
Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Shower and cooker circuits shown as 2.5mm2 on shedule but overall condition satisfactory
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
UKMeterman,
Last reply from
Pauls0212,
Replies
10
Views
1,958

Advert