Discuss Shower EICR Code- 9.5kW- 40amp mcb!. De rate MCB to 32 or rewire cable to 10mm in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

CM 1

-
Reaction score
7
Argument at work!
on an EICR its common to find a 9.5kW shower wired in 6.0mm T/E with a 40 amp MCB.
obviously a code 2 unless short run and clipped direct?
Our argument is whether to down rate MCB to a 32amp or rewire the circuit in 10mm?
I say ok to down rate the MCB as

cable is 32amp IEE say must take 1.45 times rating for 1 hour and not exceed 60 deg C also 32amp mcb will take this current
others say rewire shower in 10mm, I would agree if new install, but on an EICR it would reduce the coding to a C3 and I would note " Circuit derated and a shower rewire desirable?
 
The 32amp mcb will likely trip on overload as 9.5kw is 39amps at 240v or 41amps at 230v. Advise a down rate size of shower to suit cable or they need to upgrade it to 10mm2 for the 9.5kw
Is there any signs of over heating at all the terminals?
 
The mcb may never trip depending on the time taken in the shower however overloading the mcb at regular intervals during different days will eventually lead to heat/damage to the mcb and a possible fire risk.

As a shower is a fixed load, overload protection shouldn't be an issue or necessary if the circuit and protective device are designed and installed properly
 
The 32amp mcb will likely trip on overload as 9.5kw is 39amps at 240v or 41amps at 230v. Advise a down rate size of shower to suit cable or they need to upgrade it to 10mm2 for the 9.5kw
Is there any signs of over heating at all the terminals?

32amp mcb will run at 39 amps for an hour easily , no sign of overheating at terminals.
We come across lots of these as we do a lot of local authority work, i always down rate the MCB and have never been back to one tripping MCB !
The cable is covered by the MCB
 
There are installation methods where the existing set up could be considered acceptable however, doing an EICR you can rarely verify the full extent of the cable route to assess this so I tend to consider worse case scenario and Code it appropriately.
 
There are installation methods where the existing set up could be considered acceptable however, doing an EICR you can rarely verify the full extent of the cable route to assess this so I tend to consider worse case scenario and Code it appropriately.

Ah yes but you missing the point? No doubt it’s a code 2 to me unless can verify the installation method for the entire cable run, but I would put a 32amp MCB to protect the cable , the shower won’t trip the MCB for over an hour and would advise on the cert that the shower needed rewiring when possible
 
We would never justify fitting a lower powered shower as many properties tested have this problem , and we may have fitted the showers previously lol
 
Would surely be a cheaper/quicker fix than rewiring though? And a better option than down rating and therefore overloading a breaker (lets be honest this would be poor design!).
 
Not sure on what long term effects will have on the protective device operating on over maximum load? Particularly if someone decides to have a long shower....like my sister did once and nearly set fire to the DB with a 30amp fuse wire!
 
Not sure on what long term effects will have on the protective device operating on over maximum load? Particularly if someone decides to have a long shower....like my sister did once and nearly set fire to the DB with a 30amp fuse wire!
Lol! Definitely not safe on fuse wire , but on an MCB I think it’s ok as the only problem would be possible tripping if a V long shower was taken
 
Ah yes but you missing the point? No doubt it’s a code 2 to me unless can verify the installation method for the entire cable run, but I would put a 32amp MCB to protect the cable , the shower won’t trip the MCB for over an hour and would advise on the cert that the shower needed rewiring when possible
answer. change the shower or change the cable .
 
I just thinking of the heating effects to the mcb when it's under load, it's bound to have a deteriorating effect on the mcb, I suppose as long as you write down on the report what you advise and cover yourself, but personally I think the shower is too big for the circuit cable size.
 
I just thinking of the heating effects to the mcb when it's under load, it's bound to have a deteriorating effect on the mcb, I suppose as long as you write down on the report what you advise and cover yourself, but personally I think the shower is too big for the circuit cable size.
I agree if new installation , but on an EICR i believe it would be a C2 with the 40 amp mcb and unsatisfactory but with the 32 it would reduce to a C3 and would put a note that needed rewiring when possible?
 
Are you trying to "remedy" this to Code 3 it as opposed to putting it as a Code 2 and worry about it afterwards if remedial are required.
 
trying for a C3 as opposed to a C2 I believe by down rating the MCB and advising our client of the need for it to be rewired when possible we are complying
 

Reply to Shower EICR Code- 9.5kW- 40amp mcb!. De rate MCB to 32 or rewire cable to 10mm in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...
Replies
14
Views
3K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
635
Another what code! This is in conjunction with an EICR I have just carried out. 9.5kW shower on 6mm and 32A MCB. Been in place for a long time...
Replies
8
Views
3K
Hey all, Could do with some help. I had a company recommended to me who quoted me to do an EICR on my rental property. (£265). I thought this...
Replies
5
Views
2K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock