So you want to rewire the installation for 3 phase supply, what voltage do you want to work at 400V LL or 415V LL, you need to take in account load balancing so its not just a case of installing a 3 phase panel board or DB and connecting the final circuits in hope.

If you can split the loads evenly across each phase then you will be looking at 107 amps per phase.
But you have to take account of the types of loads, are they linear or Non linear, do you have a lot of motors.

The generator must be able to handle any starting currents for motors etc, and if the load is constant then you have to take into account that generators are more efficient when running around 80% of full load.

And trying to ramp on a load greater than 30% at any single time does cause issues, it will definitly slow the engine or if it is greater than 40% full load could shut it down.

FYI, 3 phase 400V 107amp load, to ensure you are covered would have to be minimum 110Kva, that provides approx 158 amp per phase at full load. Take into account also derating factors for ambient temp, altitude etc.
 
So you want to rewire the installation for 3 phase supply, what voltage do you want to work at 400V LL or 415V LL, you need to take in account load balancing so its not just a case of installing a 3 phase panel board or DB and connecting the final circuits in hope.

If you can split the loads evenly across each phase then you will be looking at 107 amps per phase.
But you have to take account of the types of loads, are they linear or Non linear, do you have a lot of motors.

The generator must be able to handle any starting currents for motors etc, and if the load is constant then you have to take into account that generators are more efficient when running around 80% of full load.

And trying to ramp on a load greater than 30% at any single time does cause issues, it will definitly slow the engine or if it is greater than 40% full load could shut it down.

FYI, 3 phase 400V 107amp load, to ensure you are covered would have to be minimum 110Kva, that provides approx 158 amp per phase at full load. Take into account also derating factors for ambient temp, altitude etc.

Question was asked in Jan 2022 and the OP hasn't replied since.
 

Reply to single phase to 3 phase in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock