Hey what kilowatt showers can be feed off 6mm cable and which need 10mm? I guess the distance from the fuse board also needs taking in to account?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Size of shower cable in the UK Electrical Forum area at ElectriciansForums.net
Genuine mistake and he gets abused ie accused of being a dxck lol
I have to laugh because you couldn't make it up :6:
Shocking that it is allowed to happen. I just got banned for starting a harmless thread in which I even said I was only joking. It will be interesting to see what is dished out after reading some of these replies.
beat me to it. using 230V will give a worse ( higher) value for current than using the actual ( 235 -240V ) so errs on the side of caution.
Wrong.
7kW @230=7.55Ω=30.43A
220V=29.11A 6.4kW
240V=31.75A 7.62kW
250V=33.08A 8.2
The resistance is regarded as constant.
so, power output varies with the voltage.
Hi-Geordie, hows you doing bud?Morning Tony ... You're up early.
Ohms law= current in proportion to potential difference (voltage) if temperature is constant.