Does anyone have experience sizing cable tray/ basket and trunking which is used for twin and earth cabling?

The on site guide only provides guidance and factors where single core PVC cables are used.

I am looking for help where twin and earth is used.
 
Does anyone have experience sizing cable tray/ basket and trunking which is used for twin and earth cabling?

The on site guide only provides guidance and factors where single core PVC cables are used.

I am looking for help where twin and earth is used.

What sort of trunking, plastic, metal can't understand why you would want yo run T&E in trunking unless it was for switch drops etc
 
Does anyone have experience sizing cable tray/ basket and trunking which is used for twin and earth cabling?

The on site guide only provides guidance and factors where single core PVC cables are used.

I am looking for help where twin and earth is used.

What sort of trunking, plastic, metal can't understand why you would want yo run T&E in trunking unless it was for switch drops etc

I was mainly thinking of basket but wondered how trunking would be sized with T&E. I have come across it on some supermarket installs.
 
only cowboys or house bashers put twin in trunking.
I've just finished a 1.5 storey extension on Monday with a cinema room downstair
ran basket on brackets in the coomb with 1x for power t&e and1x for data hdmi ,speakers etc
reason?
i didn't want it all covered in 4ft of insulation and I wanted to keep the power and data stuff as far apart as possible .
looked very neat and tidy and was easy to install
and I didn't have to clip a shed load of cables to every joist.
so am I a cowboy or house basher then?
 
sizing containment for T&E

I appreciate all the comments but as usual the thread is going off on a tangent. Does anyone know a reasonable method for sizing containment for T & E?
 
basket or tray, just use trhe rating factors e.g. cables touching/separated, etc. for trunking, use common sense. rate cables according to method B and don't overcrowd the trunking.
 
OP until you provide how many and what size t&e you are referring to you will not get a answer. At the minute your question is equivalent to how long is a piece of string.
 
OP until you provide how many and what size t&e you are referring to you will not get a answer. At the minute your question is equivalent to how long is a piece of string.

Its a generic question. how dies one calculate how many Twin and Earth cables can fit on x size cable tray. Yes I know you can work out the diameter if the cable and multiple, but in reality cables are not butted right up to each other. Is there a factor that is applied.
 
Like I already stated the OSG only provides guidance for single core cables.
so use the same tables. you won't be far out. as to how many cables, basically there should be approx. 50% cable and 50% airspace in the trunking. or.................. when you can't get the lid on, you know it's too full.
 
Last edited by a moderator:
Like I already stated the OSG only provides guidance for single core cables.
so use the same tables. you won't be far out. as to how many cables, basically there should be approx. 50% cable and 50% airspace in the trunking. or.................. when you can't get the lid on, you know it's too full.

How can you use the same tables when its completely different type of cable.

Come on guys do any of you actually carry out design work or do you just guess and hope for the best.
 
Its a generic question. how dies one calculate how many Twin and Earth cables can fit on x size cable tray. Yes I know you can work out the diameter if the cable and multiple, but in reality cables are not butted right up to each other. Is there a factor that is applied.

Well seeing as neither the BGB or OSG have any info regarding this then no there isnt.
 
like i said. use the tables for singles and assume T/E is poorer at heat dissipation due to it's sheath so derate by a factor that you determine using common sense. BS7671 is not the bible.( even if IET think it is)
 
like i said. use the tables for singles and assume T/E is poorer at heat dissipation due to it's sheath so derate by a factor that you determine using common sense. BS7671 is not the bible.( even if IET think it is)

Will you please re read the OP. I am not looking for cable size. I'm looking for tray size.
 
Last edited by a moderator:
How many cables? More information needed.

Also, @ the earlier posters that poo-pooed the twin and earth in trunking, I have worked on student accommodation where 4x4 trunking run around the ceiling/ wall joint and drops done in mini -trunking, wired in Twin. Also office space where all runs done in twin from DB up into attic space, along tray, boxed in drops in corners to skirting dado, etc..

Making generalisations just shows lack of real life situations.
 
Find this hard to believe....a construction company will have submitted a cable schedule and the design for containment...The normal schedule will always be for lsf singles in supported galv trunking, db armored on tray size to suit quantity plus future additions. And basket suited for data, and basket for fire/security. For all those who keep harping on about escape route containment, this is why designers have chose this method over the past 5 plus years
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
sizing containment for T&E
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
92
Unsolved
--

Advert

Thread statistics

Created
atm84,
Last reply from
davesparks,
Replies
92
Views
19,621

Advert

Back
Top