Does anyone have experience sizing cable tray/ basket and trunking which is used for twin and earth cabling?

The on site guide only provides guidance and factors where single core PVC cables are used.

I am looking for help where twin and earth is used.
 
Does anyone have experience sizing cable tray/ basket and trunking which is used for twin and earth cabling?

The on site guide only provides guidance and factors where single core PVC cables are used.

I am looking for help where twin and earth is used.

What sort of trunking, plastic, metal can't understand why you would want yo run T&E in trunking unless it was for switch drops etc
 
Does anyone have experience sizing cable tray/ basket and trunking which is used for twin and earth cabling?

The on site guide only provides guidance and factors where single core PVC cables are used.

I am looking for help where twin and earth is used.

What sort of trunking, plastic, metal can't understand why you would want yo run T&E in trunking unless it was for switch drops etc

I was mainly thinking of basket but wondered how trunking would be sized with T&E. I have come across it on some supermarket installs.
 
I can understand the use of basket for t&e but certainly not trunking. No point in it whatsoever.
 
only cowboys or house bashers put twin in trunking.
I've just finished a 1.5 storey extension on Monday with a cinema room downstair
ran basket on brackets in the coomb with 1x for power t&e and1x for data hdmi ,speakers etc
reason?
i didn't want it all covered in 4ft of insulation and I wanted to keep the power and data stuff as far apart as possible .
looked very neat and tidy and was easy to install
and I didn't have to clip a shed load of cables to every joist.
so am I a cowboy or house basher then?
 
sizing containment for T&E

I appreciate all the comments but as usual the thread is going off on a tangent. Does anyone know a reasonable method for sizing containment for T & E?
 
basket or tray, just use trhe rating factors e.g. cables touching/separated, etc. for trunking, use common sense. rate cables according to method B and don't overcrowd the trunking.
 
basket or tray, just use trhe rating factors e.g. cables touching/separated, etc. for trunking, use common sense. rate cables according to method B and don't overcrowd the trunking.

I'm not looking to size the cable, I'm trying to ascertain how many cables can fit on the basket/ tray or in the trunking.
 
OP until you provide how many and what size t&e you are referring to you will not get a answer. At the minute your question is equivalent to how long is a piece of string.
 
OP until you provide how many and what size t&e you are referring to you will not get a answer. At the minute your question is equivalent to how long is a piece of string.

Its a generic question. how dies one calculate how many Twin and Earth cables can fit on x size cable tray. Yes I know you can work out the diameter if the cable and multiple, but in reality cables are not butted right up to each other. Is there a factor that is applied.
 
Like I already stated the OSG only provides guidance for single core cables.
so use the same tables. you won't be far out. as to how many cables, basically there should be approx. 50% cable and 50% airspace in the trunking. or.................. when you can't get the lid on, you know it's too full.
 
Last edited by a moderator:
Like I already stated the OSG only provides guidance for single core cables.
so use the same tables. you won't be far out. as to how many cables, basically there should be approx. 50% cable and 50% airspace in the trunking. or.................. when you can't get the lid on, you know it's too full.

How can you use the same tables when its completely different type of cable.

Come on guys do any of you actually carry out design work or do you just guess and hope for the best.
 
Its a generic question. how dies one calculate how many Twin and Earth cables can fit on x size cable tray. Yes I know you can work out the diameter if the cable and multiple, but in reality cables are not butted right up to each other. Is there a factor that is applied.

Well seeing as neither the BGB or OSG have any info regarding this then no there isnt.
 
like i said. use the tables for singles and assume T/E is poorer at heat dissipation due to it's sheath so derate by a factor that you determine using common sense. BS7671 is not the bible.( even if IET think it is)
 
like i said. use the tables for singles and assume T/E is poorer at heat dissipation due to it's sheath so derate by a factor that you determine using common sense. BS7671 is not the bible.( even if IET think it is)

Will you please re read the OP. I am not looking for cable size. I'm looking for tray size.
 
Last edited by a moderator:
Look! It's really simple, first decide if you're grouping these cables or are they to be spaced? Then measure said cables with or without spacing, choose tray/ basket and determine size and divide this by size and number of cables. It's not hard is it?
 
How many cables? More information needed.

Also, @ the earlier posters that poo-pooed the twin and earth in trunking, I have worked on student accommodation where 4x4 trunking run around the ceiling/ wall joint and drops done in mini -trunking, wired in Twin. Also office space where all runs done in twin from DB up into attic space, along tray, boxed in drops in corners to skirting dado, etc..

Making generalisations just shows lack of real life situations.
 
Find this hard to believe....a construction company will have submitted a cable schedule and the design for containment...The normal schedule will always be for lsf singles in supported galv trunking, db armored on tray size to suit quantity plus future additions. And basket suited for data, and basket for fire/security. For all those who keep harping on about escape route containment, this is why designers have chose this method over the past 5 plus years
 
Then do it correctly, T&E is for domestic....and nowhere have I every seen it being used in the commercial sector.
 
Why is it appalling? Its perfectly fine, its only the dinosaurs that find it hard to accept.

Its designer who have respect for correct installation, and the ability by correct design, to protect the occupants and people who will be using such a building. Such standards in supported containment is a must in modern buildings. And due to its success, is now entering into domestic and HMO, IMO not before time. Correct containment save lives.
 
Then do it correctly, T&E is for domestic....and nowhere have I every seen it being used in the commercial sector.

I Guess you haven't seen everything then have you?

As I have stated, i have seen it used (specified) commercially.

You are making rash generalisations and value judgements about the use of a certain type of cable and I would have expected better from a moderator TBH.
 
From commercial to shopfitting, you throw T&E across a false ceiling without containment and BC will insist you rip it out....

I don't think this is what is being suggested. T+E (normally LSF) is used in the commercial sector and the new installs that I have been part of (and in some cases specified) have been installed in basket or on tray and are well supported throughout their run.

I agree that there is no excuse for slinging cables of any type over a suspended ceiling, but fire alarms, data and telecoms are all as guilty as anyone else in my experience.
 
From commercial to shopfitting, you throw T&E across a false ceiling without containment and BC will insist you rip it out....seen this time and time again. But electricians keep doing it, as the last posts prove..
You expect better from a Moderator...? you just have

You made the following statement

Then do it correctly, T&E is for domestic....and nowhere have I every seen it being used in the commercial sector.

The wording and meaning is pretty clear, your saying T&E cable should not be used outside Domestic Installations and your wrong, so you try to twist it and bring the word containment into play to cover your bold statement.

If you have never seen T&E used in commercial Installations then you have not worked on half as many jobs as me over the past 30 years.

Its not a competition to try and out do people that my way is the only way.



 
Then do it correctly, T&E is for domestic....and nowhere have I every seen it being used in the commercial sector.

I have to say that this surprises me.
I have seen PVC T&E specified and installed in buildings such as schools, hospitals, offices, libraries, health centres, commercial and industrial rented units, factories, and warehouses.
As long as it is properly managed then it can be entirely appropriate cable to use outside of domestic work.
 
Every specification for schools and commercial, We have tendered for have always been the same.
Tray for SWA, Gav trunking for Power/lighting, basket for data/fire/security.....Cable schedule always states LSF singles....I have not come across T&E being request or specified in and major project over the past 5 years.
 
Every specification for schools and commercial, We have tendered for have always been the same.
Tray for SWA, Gav trunking for Power/lighting, basket for data/fire/security.....Cable schedule always states LSF singles....I have not come across T&E being request or specified in and major project over the past 5 years.

Well every LA has different methods and specifications, which change frequently in my experience. And to be fair to you I have not been involved in a large project, such as I mentioned, within the last 4 years. Just my experience within the sector has seen me install many miles of PVC and LSF T&E to specification on commercial jobs.
 

Reply to sizing containment for T&E in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
711
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, I was called out earlier today to a house where a plumber was fitting a new mains electrics shower. He wanted to know if the existing...
Replies
20
Views
3K
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
930
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
239

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top