Not sure you will have to look in the good old BRB or OSG. There is a minimum distance for seperating gas and electrical supplies and i think it is 150mm, but i am working from memory, no doubt someone will enlighten us.
Cheers...........Howard
Is there a regulation on how far a socket should be from a gas pipe or gas meter?
(BS 6891:2005 installation of low pipework in domestic premises, clause 8.16.2)
Where gas installation pipes are not separated by electrical insulating material from electrical equipment, including cables, they are to be spaced as follows:
  1. At least 150 mm away from electrical equipment (meters, controls, accessories, distribution boards or consumer units)
  2. At least 25 mm away from electricity cable.
Cheers!
Cheers!
Would this be the same for Water? Sorry I don't have my BRB at the moment.
Bs 7671 (2008) aka Big Red BooK (brb)
Reply to Socket Near Gas Pipe in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi guys I am working in a warehouse where there is an inactive gas pipe and disconnected gas meter. The DB which has been upgraded now is on the...
Hi I’m getting a new kitchen fitted, there’s a existing socket outlet fitted into a pipe chase, for the rewiring of new socket outlets is it...
Hi Guys Would I be correct in thinking an electric cable can be as close as 25mm to a gas meter ? (not that I'd ever be that close out of...
Hi all. I'm currently building an island in my kitchen which will contain a gas hob. I've cut a trench about 60mm wide from the edge wall to...
Hi folks, I have recently had a 5kW Solis inverter and 15kW/hr of batteries installed. Everything is working fine, but I have some concerns about...