not permanently. i would advise the "instructed/skilled person" in charge that the installation should be turned off when not in use.
 
Quite Tel,
The install should be shut down when not in use!
Believe it or not this is a requirements of the CoP IIRC.

However, it is not uncommon in certain industries for contactors to stay energised for years on end 24/7/365.
 
I stand corrected!, thought that only applied to machines, diddnt realise it applied to sockets etc. thanks for the info!
 
I had to do a job once where they wanted an emergency button which when operated, energised a normally closed relay, which then opened, thus breaking the power to all the various bits of equipment.

Ther were a few red faces when i pointed out that should the mcb controlling the emergency stop circuit trip (yes it was a different one) , and nobody noticed... then the emergency stop button will become useless.

Hard to believe people paid far more money than I, can come up with this crap.
 