Hi Guys,

Looking for some options to provide surge protection to a 100a TPN sub main to be wired 60m from the origin

Im currently looking at installing a 4 way TPN mccb panel board with spd at the origin but it looks as if its going to cost the best part of a grand

This is obviously a far greater cost than installing a TPN 100a switch fuse but don’t really see many alternatives

Any one any ideas to keep the cost down?
 
Is there already some board at the source?

If it is simply a sub-main from supply point to the existing DB then just put in a switch-fuse for cable fault protection (assuming not TT!) at the source and then have the SPD at the end DB.

MCCB panels are expensive, and unless you get the fancy and expensive electronic MCCB (maybe with EL trip) they have a lower and harder to meet Zs requirement compared to the good old fuse.

If you absolutely have to have the SPD at the source then you could use a switch-fuse for the 100A over-current protection and then have a small DIN box for the SPD and a few Henley block to join it up, or some DIN terminals that can accept the size of incoming and outgoing wires as well as the link to SPD, or some line-taps in the DIN box, etc. Just keep the cables from block to SPD short (less then 25cm).
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
SPD for TPN 100a sub mains
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
sparky1888,
Last reply from
pc1966,
Replies
2
Views
1,493

Advert

Back
Top