Hello Everyone.

I had to change a socket in a landlord property (enough said)

Did a check on the RCD and found that it was not working.

Even though the flat only has an old 4way wylex the land lord will not go for a new board.

so my question is what tests would I need to carry out for this job if I just replace the RCD.

I.E would this come under minor works?

Thanks
 
so my question is what tests would I need to carry out for this job if I just replace the RCD.

I.E would this come under minor works?

There are a standard set of tests that you'll need to do (see GN3) to satisfy BS7671 and Building regs.

A MWC will most likely need to be issued after the work has been completed.
 
it's a like for like repair, so not notifiable, but basic testing ( Zs, IR, RCD ) and a MWC. IMO.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Southend on Sea
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Stand Alone RCD
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Mfctitch,
Last reply from
telectrix,
Replies
4
Views
1,847

Advert

Back
Top